I am wiruig a circuit very similar to page 9 in this manual using the 440 DI http://literature.rockwellautomation.com/idc/groups/literature/documents/sg/440r-sg001_-en-p.pdf

I need an indication from each contactor back to the plc though and I am using 700-HPS relays which are only 2 pole double throw.

In a setup like this since there are 2 relays in series breaking the same load and are redundant do they need to be the positive guided red control relays like the 700-HPS or could a standard 700 series relay be used that has 3 poles?
 
When you say contactor, are you referring to the 700-HPS units?

Even though it's tempting to use a standard relay you'll still need to use a positive guided safety relay. A standard relay can have a welded contact and not indicate that condition. A positive guided relay will not have this problem.

If you need more contacts in a small form factor safety relay, Omron also has a line of small PCB and socket safety relays (G7SA) that come is a wide variety of contact arrangements.
 

Similar Topics

I am working on a program that was developed in 2015 for an S7-300 safety PLC. The new copy of this machine uses an S7-1500 safety plc. We were...
Replies
4
Views
1,872
Hi, We are developing a safety system containing a emergency stop and some limit switches on some lids. We want a switch to be able to mute the...
Replies
2
Views
708
Safety for a motion system that is like 30ft+ in the air and not normally accessible? We are looking at designing a sprayer that moves back and...
Replies
7
Views
2,069
We have a legacy winch system that was built back in 1975, we are looking to replace all the controls (electrical) on this and bring it up to...
Replies
8
Views
1,914
I am working on a very large machine at the present time. This machine has several safety zones and up to 8 light curtain guarded areas. It is...
Replies
31
Views
9,711
Back
Top Bottom