I have an application where the customer would like to have a window (pop up/faceplate) open given certain states of field devices. For example if the PLC receives a certain pressure from a transmitter, or feed back from a valve position switch.

Also, under certain conditions if the pop up is active, valves may force open or closed.

So..can this be done? Using a Allen Bradley Compact Logix and PanelView HMI.

Thanks!

Burch
 
It sure can. You would just use the visibility of the object to determine when the object is to show up on the screen. You can tie that to a tag so when a tag is true then the object will show up.
 
If you want to open a popup window based on tags in the PLC, you need to use the display number and global connections. Have a read up on both of those - essentially, you assign all of your displays a unique number in the Display Properties page, set up a tag in your global connections to be a "go to screen" tag, and then use your PLC to write the desired screen number into that tag.

An important thing to remember, is that while your PLC is calling for "screen 5", the operator can't change to any other screen - it's locked to screen 5. In the global connections you can also specify a tag to be "current screen number" - basically the HMI writes the current screen number to this tag. I generally use this as a handshake - my PLC calls for screen 5, once I see that it's displaying screen 5, I call for "screen 0" again (calling for "screen 0" gives the screen control back to the operator).

Hopefully that'll get you started!
 

Similar Topics

Adding ethernet equipment to an existing panel that has none. We have some solid ethernet cables coming from other remote cabinets that I plan to...
Replies
2
Views
45
I'm trying to control a device via MODBUS RTU and the ModbusRtuMasterV2_PcCOM in Twincat 3. I've configured a device with the right com port and...
Replies
7
Views
156
Hi, I'm trying to use the IO Device Library (Product Versions) which is configured to work with the 1756-EN4TR & 1756-EN2TR but my system uses...
Replies
0
Views
48
Hello, As part of our project, we are using an M241 controller. This controller interfaces with an industrial computer and a router via a switch...
Replies
2
Views
93
I'm trying to write a data in Arduino using MODWR function block .I used the code I got from online for both PLC and Arduino. I made the wiring...
Replies
4
Views
90
Back
Top Bottom