Hi Guys,
Would you please have a look to the attached photo and let me know How to get rid if this error?
Thanks

uXmrNXZLFmTQlb21Ya6ZZkorEhaSSN9J6685UJB3M5wYd3ajHInneaEouRToYr9M8G5yfvPmFTPxfNiO1YShS9qAAAAAASUVORK5CYII=


Untitled1.jpg
 
Last edited:
Do you have a 1769-ECR end cap installed ? None of the connections on the 1769 Compact I/O bus will work without the end cap in place.
 
You need an end cap.

The 1769-ECR is the right-side end cap, which should be appropriate for your installation unless you used a right-to-right bus extension cable.

RA got tired enough of explaining this that they started including 1769-ECR end caps with the 1769-L2 series controllers, but your 1769-L31 comes from an era when you had to buy all the components separately.
 
Ken,

What I have is a L31 controller with couple of i/o card. Based on your info I will not be able to communicate with I/o because of end cap. Is that right? If so, is there any other way to communicate with i/o?

Thanks
 
You must install a 1769-ECR end cap for the 1769 I/O bus to work.

There are no alternatives to the 1769-ECR end cap.

There are no software settings that you can make to change the requirement for the installation of the 1769-ECR end cap.

The 1769 end cap is required for all controllers and network adapters that use the 1769 I/O bus. This includes the 1769-ADN and 1769-AENTR, as well as MicroLogix 1500 and CompactLogix controllers.

There is also a 1769-ECL left-side end cap that is used in some applications where a bus extension cable is used. It is less common than the 1769-ECR but performs the same function. It is not appropriate for your application if you are not using bus extension cables.
 

Similar Topics

I am having some problems with a redundant PLC setup using A/B 1765-L62 & SRM/B modules. Due to operational requirement our service engineer can...
Replies
3
Views
9,628
Hello All, I have ControlLogix L81E with with PA50 Power supply, when I power-up the PLC, I have this fault : Major Fault T01:C061 non...
Replies
4
Views
3,093
I've recently replaced an 1756-L72 and 1756-ENBT with a 1756-L81E & 1756-ENBT2R on a ControLogix chasis. The machine ran fine for two days after...
Replies
5
Views
1,673
I have a 1756-L62 that is sending a message to give a 1769-L24ER a permissive bit to run. This system has been working fine for about 2 years...
Replies
4
Views
3,754
We are doing a conversion from a PLC 5 to controllogix. There are 4 remote racks in the system. Everything was working perfect until we upgrade...
Replies
2
Views
1,770
Back
Top Bottom