Hey Everyone,
I am have a machine that runs using GE Fanuc 90 30 series PLC and I am using using Proficy Machine Edition 6.0 to be able to connect to the PLC with my computer. When the I bought the machine it had a program on the PLC, so my engineer have uploaded it, but there are a lot of things that he had removed from the PLC design, but we still have the Original project. Now the engineer has left.
The problem is whenever I try to download the original project to make the Machine as it used to be when it first came. it gives an error in the faults table saying, No user program present in Rack 0.Slot 1, which is the CPU364 that I am using. I downloaded the error code list of this series, but I don't know what it means by the description and correction in the error list.
Description:
The Fault Group No User Program Present occurs when the PLC CPU is instructed to transition from STOP to RUN mode or a store to the PLC and no user program exists in the PLC. The PLC CPU detects the absence of a user program on power-up. The fault action for this group is Informational.
Correction:
Download an application program before attempting to go to RUN mode.
What does it mean by an application program? And how to download it?
Thank you in advance
I am have a machine that runs using GE Fanuc 90 30 series PLC and I am using using Proficy Machine Edition 6.0 to be able to connect to the PLC with my computer. When the I bought the machine it had a program on the PLC, so my engineer have uploaded it, but there are a lot of things that he had removed from the PLC design, but we still have the Original project. Now the engineer has left.
The problem is whenever I try to download the original project to make the Machine as it used to be when it first came. it gives an error in the faults table saying, No user program present in Rack 0.Slot 1, which is the CPU364 that I am using. I downloaded the error code list of this series, but I don't know what it means by the description and correction in the error list.
Description:
The Fault Group No User Program Present occurs when the PLC CPU is instructed to transition from STOP to RUN mode or a store to the PLC and no user program exists in the PLC. The PLC CPU detects the absence of a user program on power-up. The fault action for this group is Informational.
Correction:
Download an application program before attempting to go to RUN mode.
What does it mean by an application program? And how to download it?
Thank you in advance