Dear all

Is phase sequence in Star Delta starter necessary, Just i got flash with wrong phase sequence.can anyone tell me how to know the phase sequence if i am starting first time???
 
Type in Star/Delta wiring diagram into google, but if you do not know what you are doing get someone who does, otherwise you may do some serious damage.
 
the current in delta should have same direction as the star situation.
this is why the connections are not U1,V1,W1 and U2,V2,W2
but V2,W2,U2
so you put L1 on U1 and V2 etc. find a connection diagram and simulate the phases
 
If you manage to swap a phase when changing, you got a wiring error.. Check your diagrams and consider getting someone who knows what they are doing...

Did you remember to take out the inserts from the termination terminals in the motor?
 
Did the flash occur when it first started in star or did it occur
as it transferred from star to delta.

Take a photo of the motor terminal box for us to see.

Finding someone who knows about star delta starters and motors
is your best option though.
 
Is this motor US or EU? Your peckerhead should have a diagram of what pins go to what. I agree with the above post, give us a solid pic of the motor and we can tell you where to land what. You crossed a phase somewhere you shouldn't have :(.
 
Gyus motor is from Itlay.when i first started it got flash. I checked the connection at TB side there it was burn at V2 and W2.when i changed the V2 to W2 it works.I could not understand why it git flash in first situation???
 

Similar Topics

Hi, We have a project to replace one Star Delta connection for 90kw motor (3 phase, 415V) with an Inverter. Before dismantle the S/D, the current...
Replies
14
Views
10,548
HI EXPERTS SOMEBODY ASKED ME TO CHANGE THE ROATION OF A STAR DELTA 3 PHASE MOTOR HOW THIS IS POSSIBLE ON A REGULAR DIRECT ON LINE STARTING...
Replies
4
Views
11,386
Here's a question I thought I'd never ask with all my 50 years of experience but I don't know - so I'm asking. I have to change a star delta...
Replies
23
Views
3,148
Found that a trouble some pumps that kept causing overcurrent faults on the VFDs were wired in star instead of delta configuration. In star...
Replies
6
Views
2,615
Hi all, Got a customer who's asked me to look at a new machine they've gotten in which they're having trouble starting. It's a brand new...
Replies
10
Views
4,254
Back
Top Bottom