I'm trying to configure Altivar 312 VFDs, but my safety circuit drops 3-phase input and currently that also causes the logic/communications to go down as well. All the documentation I've looked at seems to indicate the 24VDC on the drive is and output to provided a convenient source for the logic inputs. I'm wondering if I can back drive this to power the logic side of the drive without hurting it.

I'm just sitting on my hands right now since all the guard doors are open and I need to be troubleshooting a communications issue.
 
The safety circuit should not drops 3-phase input but only the power to Motors starters, Drives, Valves Etc. All the PLC inputs, communicatios etc. should maintain power.
 
@CapinWinky - Looking at the manual, I would say no. The 24VDC source on the terminal strip is internally protected and limited to provide up to 100mA out, so I seriously doubt you could backfeed it to power up the control board.
 
Good point, I would imagine there are some diodes in there that will prevent backfeed. I may still try it since we have a drive that may need to be RMAed anyway; if I do, I will report here.
 

Similar Topics

Hello everyone. I'm trying to communicate a Controllogix L36ERM with a 1769-SM2 Modbus module to a Schneider-electric Altivar 312 Modbus motor...
Replies
7
Views
2,479
Hi all, i have a S7-1200 with a CM1241 and i want to control 10 Altivar312 Inverters. Does anyone have a good working sample?
Replies
2
Views
2,540
Hey All, I have a little retro project going on that involves Modbus control of some Schneider Altivar 312 VFD's. I have done a couple of...
Replies
8
Views
4,068
I'm doing a new Elau/PacDrive3 system and I'm trying to decide which VFD to use. The issue is, the 312 is $150 cheaper per drive, but doesn't have...
Replies
1
Views
2,063
All, We have a site that has multiple Altivar 66's that are being controlled by an old Square D Modbus+ network. One of the VFD's has failed...
Replies
2
Views
367
Back
Top Bottom