4-20 mA water level sensor

karlek

Member
Join Date
Jul 2014
Location
Varazdin, Croatia
Posts
68
Hope someone can help me on this :)

Currently there is hydrostatic level transmitter (4-20 mA, 2 wire current loop with 10-30 Vdc supply needed) already installed on location (headrace canal of small hydro power plant) and connected to existing PLC.

Our company is doing some upgrades and we'll have separate PLC for controlling some of the plant functions. So is it possible to connect this existing 2 wire sensor parallely to our newly installed PLC (analog input 4-20 mA) or we'll need another level sensor in order to get water level variable?
 
No- you cannot parallel a 4-20mA signal. You could run in series but I would not recommend it due to ground loop or power supply issues. The best is to get a signal splitter that will output 2 isolated signals. Phoenix, Acromag, PR electronics are a few that sell them.
 
It depends on what type of input the PLC uses, I always use 10 volt inputs and a resistor of 500 ohms , or 250 ohms.
Voltage signals can be used multiple times in paralel.
If the input is isolated from rest (so it has a mA input and a connection mA output, and not directly going to ground you can put them in series, Like the WAGO/Beckhoff has isolated channels.
Or repeat the channel to an output.
 
If the input is isolated from rest (so it has a mA input and a connection mA output, and not directly going to ground you can put them in series,
Or repeat the channel to an output.

IMHO Yes, I also would add my analog in, in series as long as I was certain of my power supply and loop isolation issues, as an old loop guy. This may not be the best method for everyone. There are definite considerations to be aware of, as with the next option, one must be aware of powered and unpowered loop requirements, isolation and power supply ratings etc...

If you have an extra analog output, (call it analog out 2) in YOUR new unit w/ imbedded I.O., you could feed the existing loop only to YOUR analog in, (keeping the powered/ unpowered concepts in mind) then, in YOUR logic, (in addition to whatever else you were going to do with the signal) move that value to your analog out 2 and feed the existing PLC's analog input with that. (Keeping the same powered, unpowered concepts in mind) i.e. "repeat"

Just my humble 2 cents,

Regards
 
Whether you parallel a voltage signal (from the dropping resistor across the analog input) to a 2nd AI or run the current signal in series to a 2nd AI, the risk is common mode voltage between the sender and either of the receivers or between the two receivers. 'Single ended' AI's are very likely to have common mode problems.

If the common mode voltage level is low, it might result in just an offset of the interpreted readings.

If the common mode is high, but not destructive, it could drive both signals off scale

If the common mode is high and destructive it could burn out either analog output.

Try it and see, but if you get a shift in the signal when you connect the wires, there's common mode.

Signal splitters typically isolate the input from the output and isolate one output from the other output, so there is no 'common' mode between the sending device and receivers, or between the receivers.
 
If you have an extra analog output, (call it analog out 2) in YOUR new unit w/ imbedded I.O., you could feed the existing loop only to YOUR analog in, (keeping the powered/ unpowered concepts in mind) then, in YOUR logic, (in addition to whatever else you were going to do with the signal) move that value to your analog out 2 and feed the existing PLC's analog input with that. (Keeping the same powered, unpowered concepts in mind) i.e. "repeat"

Just my humble 2 cents,

Regards

Yes, of course, after you acquire the signal with analog input you just feed it to to analog output (by means of software/program), I had some other thing in mind, nevermind :D

Thanks everyone for the help, now I have a bunch of directions and tips to work with.
 
Do you even need to do any of this? If the PLC's are networked you could just share the level reading across the network.
 
If the card has isolated inputs (for each channel separate in and out ) so no common ground.
both versions are available. so if 1 is in and 2 is out, you can use them in series with another PLC as the input is isolated to 4000 volts :)
they have sometimes 2 channel (they are isolated, but the 4 channel has both possibilities.
 

Similar Topics

I want to measure the level of water inside a closed st.st tank with an over flow opening in the top of the tank at the begining of filling the...
Replies
16
Views
4,719
Looking for a low water sensor for a critical application. This is a large water bath with dirty water that has some surface ripples and movement...
Replies
9
Views
5,072
We have a customer that uses a diafram pump to send water and ravioli to a hopper. The hopper then has a cogged belt that pulls them out from the...
Replies
13
Views
4,355
I have a sensor which works by passing current through water. I mean it is simply naked wire in the water tank. I use 24VCD. Ground wire is at the...
Replies
8
Views
3,919
how to Invert the Analog water Level Sensor values? It messure number in int from 27565 (tank empty) to 0 (tank Full) It there som kind of...
Replies
14
Views
6,209
Back
Top Bottom