VbSparky said:
for your valves if there is no information on them besides
the voltage measure the resistance of the coil with a ohm meter
DON'T DO THAT!
This is
AC circuit, not
DC. If there is no information on the coil itself, try to get it from the valve manufacturer.
Measuring the resistance with an ohmmeter will give you just that - the
resistance. However, in AC circuit, the current will be determined by the coil
impedance as well - and to a greater degree.
Sure, nobody will get killed if you do it this way. But the transformer will be much bigger and way more expensive than necessary.
If you know the coil's current, multiply it by the number of the coils and then by the voltage (24 Volt in your case). This will give you the total power consumption in Watts. If the coils are rated in Watts - just multiply that value by the number of the coils.
Add at least 20% safety overhead. The transformers are usually made in standard power ratings, pick the nearest one from a catalog that exceeds your result.
Edit: to be precise, your total power will be measured in VA (Volt - Amps), rather than Watts. The transformers are usually rated in Volt-Amps as well (or in kVA, which is 1000 VA). For the purpose of this exersise, the difference between Watts and Volt-Amps does not matter. Consider them two names for the same thing.