Hi All,

I am using GE module IC200MDL750 (24V Dc) in Manual(IC200MDL740.pdf) it is Written 0.5A output Load Current.
i want to ask this is for Maximum Load current(32 points) or Single output Current(1point)???

Similarly I want to know IC200MDL650(IC200MDL640.pdf) Input Current Maximum (32 points) and Single input Current(1point)
 
The current rating for the MDL740 is per point. The derating chart in the data sheet indicates the allowable ambient temperature for different orientations of the module when multiple points are simultaneously on at maximum rated current.

In the case of input modules current consumption is generally not an issue. Each circuit consumes between 2.0 and 5.5 mA in the on state and between 0.0 and 0.5 mA in the off state. At 24 VDC the module will generate 2.1 watts of heat in operation if all inputs are simultaneously energized and each circuit consumes maximum current.
 

Similar Topics

I have one GE Fanuc IC200PNS002-AC Versamax Network Interface Module and the fault red light is blinking and i have checked in manual it is...
Replies
9
Views
190
Hi, The VersaMax PLC suddenly stop running (no LED on run function) so I'm trying to upload the program. The HMI connected to it says "Host...
Replies
0
Views
128
I do have a problem with a GE Versamax micro PLC. By going online (on Port 1) the "OK led" goes down. Power led stays On Port 2 no reaction at...
Replies
4
Views
385
Hi, I am trying to set the IP address on the IC200UEM001 Ethernet Option Module. I am following the procedure in the manual for setting a...
Replies
1
Views
423
I have a new computer and it doesn't have an ethernet port. I am trying to connect to the Versamax Micro Plus with a type c to ethernet adapter...
Replies
7
Views
1,234
Back
Top Bottom