ganutenator
Lifetime Supporting Member
PLC: Modicon Quantum 113-03
I/O:
PIT (located downstream of control valve)
FIT (located upstream of control valve)
FCV (in the middle)
Basically the customer wants a flow control loop using proportional and integral. but...
Wants to add a pressure setpoint that he doesn't want exceeded.
Please tell me if this would work or if there is a better way:
I was thinking of setting up two PI loops. One with a process variable of Flow and one with Presure. Whichever told the valve to go the most closed, its output would be written to the valve.
Note: I would point both PID function blocks' "reset feedback word" at the 0-4095 value going to the control valve. Is there any problem with the one loop being direct acting and the other loop being reverse acting? I don't fully understand the feedback word except that it is supposed to help thwart integral windup while in manual.
Also, I have noticed on earlier posts that you want to have the loop update time match the pid trigger time. I believe that the modicon works like the slc in this regard and needs to be energized every scan else the integral and other params will reset. Am I correct?
Additionally, any other tips/tricks that anyone has for the Modicon PID block would be helpful. I don't understand how to use the "track input" word neither.
Thanks in Advance!
I/O:
PIT (located downstream of control valve)
FIT (located upstream of control valve)
FCV (in the middle)
Basically the customer wants a flow control loop using proportional and integral. but...
Wants to add a pressure setpoint that he doesn't want exceeded.
Please tell me if this would work or if there is a better way:
I was thinking of setting up two PI loops. One with a process variable of Flow and one with Presure. Whichever told the valve to go the most closed, its output would be written to the valve.
Note: I would point both PID function blocks' "reset feedback word" at the 0-4095 value going to the control valve. Is there any problem with the one loop being direct acting and the other loop being reverse acting? I don't fully understand the feedback word except that it is supposed to help thwart integral windup while in manual.
Also, I have noticed on earlier posts that you want to have the loop update time match the pid trigger time. I believe that the modicon works like the slc in this regard and needs to be energized every scan else the integral and other params will reset. Am I correct?
Additionally, any other tips/tricks that anyone has for the Modicon PID block would be helpful. I don't understand how to use the "track input" word neither.
Thanks in Advance!