Red Lion Modular Controller count value

Bunger

Member
Join Date
Sep 2009
Location
Connecticut
Posts
5
Could someone take a quick look at this simple program and tell me why my counter is not working.
Basically I want input 1 to advance the counter by 1 on every input.
The data logger confirms that input 1 is working but the count stays at zero.
 
I have not used the Logic Editor but a quick guess would be you have a preset of 0 and sometimes preset counters will stop counting when they reach preset
try entering a value for preset and see if that works
 
To start with, your logic editor shows that you're using inputs 2 and 5, instead of 1 and 2 as your variables are assigned.

edit: nevermind. I think you need to initialize the module conifuration to "include in download" and "Run" the logic engine.
 
Last edited:
Preset zero means that it will count to 65535 then return to zero. Do not want a preset. Confirmed that with RL yesterday.
I had already corrected my logic editor. Input 1 is the input to the counter, Input 5 is the reset on the editor only. There is no actual reset. Input 2 is unrelated to the counter.
 
Last edited:

Similar Topics

Dear sirs I'm using Red Lion products and now I have 2 problems to ask you here. 1) I use CSMSTRLE as a protocol converter [Modbus RTU to...
Replies
0
Views
1,284
I'm using Red Lion Modular PID controllers with Automation Direct Productivity PLCs and HMIs. I have 10 heating zones, each with their own module...
Replies
0
Views
1,351
In a Red Lion modular controller system with a base unit and ten two-channel loop controllers, one or more of the individual modules will...
Replies
3
Views
1,790
Hi, This is my first time trying to configure a Red Lion CSMSTRSX controller and I have bumped into a roadblock. My objective is to set up a...
Replies
0
Views
1,179
Can't find the terminating plug for an old Data Station - I get 4 blinky status lights. Is there a short term work-around until i can buy a new...
Replies
0
Views
1,589
Back
Top Bottom