Analog addressing help

andyso218

Member
Join Date
Feb 2015
Location
Toronto
Posts
5
i was wonder how i would go about addressing an analog current generator in cx-programmer that is connected from the slave drt1-ad04. The master is cj1w-drm21 and the cpu is cj1m-cpu13
 
That is the addressing range of the slave units when the Auto addressing is used with the DRM21.

The specific channel address will depend on the slave node number.
 
You should be able to view that address and see the analog input value, if the Fixed addressing scheme was used to set up the module.
These modules can also be configured for User addressing, which could move the addressing to a different location.

The W380 manual provides a lot of information on the DRM21 module and addressing.
 
I would probably start by reviewing the DRM21 setup in I/O Table and Unit Setup.
That should reveal how the module was configured and then you should be able to understand the addressing.
 

Similar Topics

I apologize if I've missed an existing thread on this topic. I have added a siemens rack to replace a Beckhoff remote IO rack and all is well...
Replies
16
Views
3,195
Good day! i would like to ask about what are the analog addresses in mitsubishi plc..the siemens s7 300 plc has PIW and PQW.. what should i use...
Replies
2
Views
1,849
The noob returns! In the attached image, you can see where I've configured a remote analog output. Where I'm having a hard time, laughably...
Replies
4
Views
1,479
Hi, In InTouch (I'm using v9.5) you can address bits of a tag like this: tagname.01 = 0; This has the advantages of only having to set up one...
Replies
2
Views
3,738
Hey. I am makeing a SCP in af micrologix 1100. But how do I addres the Input to be on of the analog inputs. thanks
Replies
3
Views
1,566
Back
Top Bottom