Selecting Transistor Board

Join Date
Jan 2015
Location
rajkot
Posts
5
8-channel-font-b-transistor-b-font-output-PLC-font-b-DC-b-font-font-b.jpg
I

want to use this 8-channel transistor output PLC DC amplifier board
for use solenoid valve 24VDC 1.5 AMP

Description
8-channel transistor output PLC DC amplifier board board protection plate separator plate non-contact relay
To isolate the controller output and field loads. Short circuit, and interference protection circuit, safe and reliable,
Operating voltage: 24V
Input signal: 5-12V
Output voltage: 24V
The amount of load current home: 5A

Is this the correct Board for switching Solenoid valve
Require to switch Maximum 5 Solenoid coils at time ???
 
Is the 5A rating per channel or for the whole board?
Be careful when switching solenoids with transistors. The spike when the field collapse can cause havoc with the transitor. You may need to add a diode to the circuit to keep that from happening.
 
No.
The inputs are rated for 5-12 volts. It should be 24 volt.
It has protection diodes on the outputs.
The 5A rating is probably the whole board.
 

Similar Topics

I am working on trying to create a an HMI program where the user can select a value from 1-25 and then enter a string, which will be placed into...
Replies
5
Views
1,054
We had a servo motor feedback cable get damaged recently and we want to order a replacement. The current cable is a custom made cable, and we...
Replies
1
Views
886
Not sure how to word the title but here's my scenario. We have a carriage that moves at high speed with an energy chain and the cable bends in a...
Replies
11
Views
2,861
Hello plctalk, new guy here. I have an application that I'd like to present for your considered opinions so I can figure out what hardware I...
Replies
11
Views
2,504
Hi, I frequently demonstrate automation product (that we make) to various customers. The system uses an AB7007 Anybus gateway that connects to...
Replies
16
Views
5,256
Back
Top Bottom