Can any one confirm for me that you can configure DASIDirect v1.5.0 to communicate to an S7-1200 over ethernet.
I've found reports of this working with DASIDirect v3.0 if you configure with the following settings. Set as S7-300 PLC with. Rack 0, Slot 1, connection resource 3, remote TSAP 3.

Also would it be be possible to at the same time have a KTP300 also connected via ethernet to the same S7-1200 PLC.

Thank you.
 
Rack 0 Slot 1 should work.
But you can only get access to "not optimized" data blocks (right click on the datablock which you want to access, and disable the option).
If you are using a 1200 with a newer firmware version, there is an option in the hardware config where you have to enable Put/Get communication to get this working. Older versions don't have this option, it's always possible.
 

Similar Topics

Hi, We are setting up an Aveva Plant SCADA node with the intention to connect it to a Wonderware Historian node. Everywhere I look online I see...
Replies
1
Views
120
Hola chicos. Tengo un problema con el driver de comucicacion dasabcip 5, y un plc controllogix v34, ya realice la comunicacion pero en ciertos...
Replies
2
Views
104
Hi, I am upgrading a Wonderware SCADA form version 9.5 to version 23. I am able to migrate all the graphic, but when to activate the runtime this...
Replies
8
Views
340
Hi all, I am using OI.GATEWAY.2 to communicate to the PLC using an OPC UA. I can see the tags using an OPC explorer connecting to the...
Replies
0
Views
129
A project recently went through to replace an old computer that was running Wonderware with a new computer. After a bit of work I was able to get...
Replies
7
Views
404
Back
Top Bottom