We are building a testcell for testing diesel gensets. The maximum rating is 550KVA@400V.

There is going to be a loadbank used for the absorption of power with both resistive and reactive loading.

We are wanting to have a contactor inline so that genset power can be isolated from the loadbank (for voltage protection, etc).

We will also be wanting to put breaker infront of the contactor to serve as overcurrent protection for the wires as well as a disconnect/lockout point.

For sizing of the contactor and breaker, is 800A sufficent?
I am thinking of using the following contactor.
http://www.factorymation.com/Products/Metasol-Contactors-150-to-800A/MC-800A-22-AC-DC200.html

For breaker, a MCCB:
http://www.factorymation.com/Products/MCCB_800_Amp_High/TS800HU-FMU-LL-800.html

How does this seem?

Thanks
 
Okay. Sorry about that. (Didn't put 3 phase in the calculator :unsure:)
You should overrate to 125% for continuous loads.
"Read the rule closely; the 125% sizing of the OCPD (or 80% loading) is only applicable when continuous loads are involved. CBs and other OCPDs can be sized at 100% of their rating for noncontinuous load applications."
Link
 
Okay. Sorry about that. (Didn't put 3 phase in the calculator :unsure:)
You should overrate to 125% for continuous loads.
"Read the rule closely; the 125% sizing of the OCPD (or 80% loading) is only applicable when continuous loads are involved. CBs and other OCPDs can be sized at 100% of their rating for noncontinuous load applications."
Link


I would consider genset testing to be noncontinuous. Especially since the 550KVA set will only be part of the testing, and will only be 100% loaded very small part of the time.

Given that, I the the previously linked breaker and contactor will work.
 
rate the mcb to be 1600 amps as it should switch off reliable.
even when shorting under max load.
as you are testing.
the normal only needs 800 as it is abnormal but the testrig is normal for overload.
 
rate the mcb to be 1600 amps as it should switch off reliable.
even when shorting under max load.
as you are testing.
the normal only needs 800 as it is abnormal but the testrig is normal for overload.


I'm sorry, but I don't quite follow with what you have said here.
 
in normal operations 800 is good, as it needs to shut down only when an error occurs (that is maybe once a year, however on a testbank this occurs maybe even every minute so then the rating is not enough.
And be sure to use a safety circuit, as it must be reliable to shut down even in overload conditions, like 200%.
 
My answer is it depends! The generator could be tested for a number of hours. Also if it has been running on low loads for some time it will need to be run for 4-6 hours from time to time to stop/eliminate glazing of the cylinders. Additionally if load dumps are being made onto the generator during testing then inrush would be high and would need to be calculated into the breaker size.
I assume that the load bank will not be dumped onto the generator but stepped on? If it is dumped on it is highly probable that the generator will stall. You would have to che3ck with the manufacturer as to what the acceptable load steps are for the generator. Normally the first step should not be more than 40%.
 
there is a procedure for testing generators, one of them is over current break. if normal breaker does not work the safety breaker on the testset must be capable of breaking at much higher current.
 

Similar Topics

Dear All, Currently I'm working for PICO Hydro system that installed at remote rural area which there have no power supply from service...
Replies
3
Views
1,455
Looking for a modbus reference for a comap IG-NT GC HW version 1.3. Any help would be appreciated.
Replies
3
Views
1,562
Reaching out to all the seasoned folks, what would you use if you were to provide a 300 kW power generation system? A diesel genset or a...
Replies
17
Views
6,168
Hi dears, we have HCI IC-900 ignition controller. we are facing problem no ignition signel from controller to coils. we have check all...
Replies
2
Views
2,732
Anyone know how the alternator splits from the perkins diesel ? I phoned Wilsons in Ireland to be told by tech support to remove the air guards...
Replies
7
Views
2,560
Back
Top Bottom