Change Processor Node Number

Mickey the configuration is Com1 SLC-CH0, Baud 19200,8,n,1. I can talk to the PLC as processor node 1 but need to change the node number so I can have more that one PLC on the link.
 
What you have posted is how RSLinx is configured, not how the PLC's comm port is configured.
The PLC's port is probably configured for DF1 Full Duplex which is a peer to peer configuration, you will not be able to talk to more then one PLC at a time.
The PLC's port will need to be changed to DF1 half duplex or DH485 to network multiple PLCs. If the other PLC's support Ethernet then that is the best way to go.
 
Thanks Mickey the PLC port is defined as full duplex, I will change it and try again.


How are the PLC's connected (networked) together?

Bare in mind if you change the comm ports protocol you will have to change the driver in RSLinx to reconnect. Or use the Ethernet port to connect.

I would stay away from DF1 half duplex if at all possible. If you must create a network using the serial port then DH485 would be best. Other hardware may be necessary though, to create the network and to get reconnected to the PLC.
 
Thanks again Mickey, I've rethought utilizing serial connections and have decided to go with Ethernet. I wanted to try the serial because the link will be a 10 mile vhf wireless link with limited bandwidth. It will be easier to limit the Ethernet traffic going through the radios than to get the AB serial link to work. thanks again
 
Thanks again Mickey, I've rethought utilizing serial connections and have decided to go with Ethernet. I wanted to try the serial because the link will be a 10 mile vhf wireless link with limited bandwidth. It will be easier to limit the Ethernet traffic going through the radios than to get the AB serial link to work. thanks again


Wise choice.
 

Similar Topics

I have a project with one CompactLogix processor and one ControLogix processor. They are on the same local network so produced and consumed tags...
Replies
3
Views
1,716
I was wondering how hard it is to change the processor type in RSLogix500. By change processor type, I mean change the processor from say a...
Replies
6
Views
7,151
Hi All, I am facing a problem in modicon premium Plc so i want to upload back up program in Plc processor 57203 . but when i am trying to do this...
Replies
0
Views
2,771
We have a packing machine with a 1785-L60L Extended Local PLC-5/60L controller with a 1785-ENET attached in the main rack and connected from the...
Replies
13
Views
3,455
Hey all, i have a panelview screen (image attached), with 4 items on it. Program 1, Program 2, ...3, ...4. The PLC i am using is a compactlogix...
Replies
5
Views
129
Back
Top Bottom