I have a new Micrologix 1400. I have an SCP instruction that should give me a 0-4095 output on O:0.5 address. Problem is it does not ever change the value from 0. If I manually type a value like 4095 into O:0.5 the output will give me 10VDC. I have even tried removing the SCP and replacing with a MOV instruction. The value of the output will not change.
 
Hello and Welcome to the forum.

Are you writing this instruction in LAD 2?

If not can you make sure you have a JSR pointed at the LAD that you are writing this instruction on.

If both of these check out, then can you post your program.
Zip it first.

EDIT: OPP's I put rung instead of LAD, fixed it with this EDIT.
 
Last edited:
The instruction is in Lad File 7. I have a JSR for U:7. Other instructions in this Lad File work. The SCP instruction has no permissives and should scale the value of an F:11 register from input 0-100 and output 0-4095. The output is not used anywhere else.
 
If your SCP has a destination of O:0.5, and your manually writing 4095 into it without it being overwritten, then "most likely" your SCP is not getting scanned. If it was, your 4095 would be overwrote with whatever the SCP calculated.

Is O:0.5 where the SCP is writing to?
 
Yes the SCP is writing to O:0.5 I tried replacing the SCP with a Move instruction. It would not transfer either. I wonr be able to zip the program and post till tomorrow.
 
If you tried a move and an SCP, it really seems like that routine isn't getting scanned although you said other logic in it is working.

update- I just looked in the Micrologix instruction help and it says floating point is not supported in the Micrologix 1400 SCP instruction.

scratch update above possibly- it says the "parameters" cannot be floating point.
 
Last edited:
I'm fuzzy on Micro's because I don't get into much anymore but that's probably why-Your trying to move a 32 bit float into a 16 bit output register. I know you can move into an integer (N) and it will round up or down, but I'm not sure that works into an output? I'm sure somebody can set us straight?
 
Also - just because the routine is getting scanned, doesn't mean it's getting all the way to that rung. There could be RET or JMP instructions involved, skipping part of the code.

Add a rung directly underneath that one with an XIC OTE. Make sure neither are used anywhere else. Toggle the XIC and the OTE should come on - if it doesn't you know that something's stopping the logic scanning down to that point.
 
I have several Micrologix 1400 using the SCP instructions with floating points as the input that work fine with the built-in analog outputs. The SCL instruction requires a interger to work. If you are using SCL try replacing with the SCP.
 
I’ve done what you’re trying to do except that the destination from the SCP was to an integer and then I moved the integer’s value to the analog output. To be fair the other difference was that everything was done in LAD 2. If you haven’t yet come up with the fix you might try changing the destination to an integer and then move it to the output. At very least you’ll be able to see if the SCP is being scanned. If the integer value changes but the output doesn’t you’ll know that the SCP is doing what it’s supposed to but something is taking hold of the output. With that said if you’ve got something in LAD 2 that is driving the output you’ll probably need to disable it when the LAD file with the SCP is active.
 

Similar Topics

Hello...I'm a pretty fluent SLC 500 programmer, but am now trying to develop a Micrologix 1400 program offline (1766-L32BWAA). I'm amazed that I...
Replies
12
Views
13,100
Howdy all, New to the 1400. I have read the manual a few times (maybe not every word) but still can not find where the embedded discreet inputs...
Replies
13
Views
12,997
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
87
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
Replies
4
Views
221
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
300
Back
Top Bottom