Point I/O Ethernet adapter or Flex I/O Ethernet adapter

jtashaffer

Member
Join Date
Aug 2009
Location
KY
Posts
415
I have a SLC 5/05 plc and I want to add a remote rack to it. Which one is easier to make work with the Slc ( point I/o or flex I/o). I want to control it over Ethernet. I will need a analog input card and a HSC (high speed counter) card.
 
The SLC-5/05 supports only unscheduled data table messaging over Ethernet and will not work with any sort of Ethernet I/O.

There are probably approaches that will work with your application to run another controller (like a MicroLogix) and exchange data with the SLC-5/05 using messaging, or to run I/O on a network like DeviceNet.
 
I I was in your position here is how I would go:
1) You may want to take this opportunity to upgrade your processor to a Compactlogix processor. You would need to install a 1747-AENTR in place of the 5/05. Then the SLC I/O would but a remote Ethernet I/P rack. Then you can add Point, Flex or 1769 I/O all you want over ethernet.
2) If price and time are a premium you could then find a RIO or DeviceNet adapter on ebay fairly cheap. Then you can use Flex I/O for your remote rack. I will warn you that Flex I/O Analog data using RSL500 is kind of a PITA. It is not nearly as nice and clean as RSL5K installations.

If you need more info post back.
 
I would like to upgrade to. I have never really used point I/O or flex I/O. I was just trying to save running conduit and wiring. I will just run it all to the control room since it is all a struggle. I thought it might be a easy setup. thanks for the info.
 

Similar Topics

Hello, I have a ControlLogix L73 at firmware 24.11, Logix Designer at version 24 I have a 1734-AENT Point IO ethernet adapter, the box says...
Replies
6
Views
1,618
I am currently setting up a work cell with a L30ER Compactlogix PLC and three Point IO sections. I set the IP address on the point IO using the...
Replies
8
Views
17,221
Anyone know off the top what the maximum cable length should be between a compact logix controller and some point I/O? I have 10 meters in my...
Replies
2
Views
1,546
Just wondering if anyone ever had this setup. I have 3 micrologix 1400 communicating via cradlepoint modems. They in turn each is hooked to a...
Replies
4
Views
1,672
Hello more knowledgable people and old friends, I'm trying (and failing) to connect a ROCON DeltaPoint to the PLC with RSLogix 5000. I tried...
Replies
16
Views
2,982
Back
Top Bottom