System is an IPC547D running GRAPH in WinAC RTX. Six S7-1200 (CPU 1215C) running a little code for manual operations, but mostly running as I-devices. 12" Comfort panel. TIA13.
I can't write to PLC6 from GRAPH in the PC. Everything else in Seq1 is working. When I get to a block that writes to Q600.0, WinAC RTX goes into Stop with an error.
I was getting a double word error for address 600. I took out the command that wrote zeros to QD600. Now it doesn't crash until I try to turn on the VFDs in the mixer - Q600.0, Q600.1, etc. I was running with OB121, but took it out to see if I could get a clearer error message.
I've checked and rechecked. PLC 6 is configured the same as the other five working PLCs.
The expert from Siemens setup the first 5 PLCs as I-Devices. I setup the sixth. I-Device box is checked, addresses are correct. I've compared with working PLCs, but just can't find it.
What did I miss?
Overview of address gaps. PLC 6 has 602 - 16383. Others are only 100 Bytes. Q 0-99, Q 102-199, etc.
Fault from PC running GRAPH:
Area length error when writing
Q area, bit access, Access address: 600
FB number: 1
Module address: 2118
Requested OB: Programming error OB (OB121)
OB not found, or disabled, or cannot be started in the in the current operating mode
I can't write to PLC6 from GRAPH in the PC. Everything else in Seq1 is working. When I get to a block that writes to Q600.0, WinAC RTX goes into Stop with an error.
I was getting a double word error for address 600. I took out the command that wrote zeros to QD600. Now it doesn't crash until I try to turn on the VFDs in the mixer - Q600.0, Q600.1, etc. I was running with OB121, but took it out to see if I could get a clearer error message.
I've checked and rechecked. PLC 6 is configured the same as the other five working PLCs.
The expert from Siemens setup the first 5 PLCs as I-Devices. I setup the sixth. I-Device box is checked, addresses are correct. I've compared with working PLCs, but just can't find it.
What did I miss?
Overview of address gaps. PLC 6 has 602 - 16383. Others are only 100 Bytes. Q 0-99, Q 102-199, etc.
Fault from PC running GRAPH:
Area length error when writing
Q area, bit access, Access address: 600
FB number: 1
Module address: 2118
Requested OB: Programming error OB (OB121)