analog cj1w-mad42

Join Date
Mar 2015
Location
bandung
Posts
11
hai, i'm nova.
can you help me, to solve the problem when i use cj1w-mad42. in the manual book said that this special I/O habe mean value processing. but, i don't know to make this program. i have already try it, but i can't find the mean value processing.

and can you help me to solve the program. i want get mean value from the analog input in 50 sample of my data. and i don't know how to make it.
 
In CX-Programmer open the I/O Table and Unit Setup from the Project Tree View on the left.
If the I/O Table has been setup, right click on the MAD42 module and click on Unit Setup.
Scroll down the parameters until you get to Inputx Mean value processing setting parameter.
You can select the value from the drop down list.
Options would be 32 or 64 buffers. 50 is not an option.

Hope this will help.
 
thank you for your information,

and, i must make it in a ladder diagram or not?
is it only setting in I/O setting or i must make ladder diagram too?

i have already examine my PLC, but i can't feel the good effect use the mean value processing.
i don't understand for using it in a program.:confused:
 
With the MAD42 set to 64 buffers you are averaging the data over approximately 285 milliseconds. If you need more averaging of the data you could use the AVG(195) instruction to read the MAD42 I/O value into an averaging buffer.
 

Similar Topics

Dear All, I want to use a 4-20mA output from Omron AO module, so I did the following configuration: PLC used CJ1M-CPU22, rack 00 CJ1W-AD041, rack...
Replies
13
Views
4,937
Hi all, I only do PLC Programming on and off and have never done programming analog stuff therefor I need a pointer in the right direction. We...
Replies
3
Views
4,539
Hi, I am looking for the datasheet or any specification document for Omron CJ1W-PDC15 analog input card. I need +/- 5V analog input card and...
Replies
4
Views
3,994
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
4
Views
57
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
7
Views
113
Back
Top Bottom