Hi
I have 2 PF525 in my office to add to my test rig and setup

I dont have 400V 3 phase... can i power these via 24V DC to just get the controls and Ethernet IP powered? I looked on the cut sheet supplied and didnt seemthat i could

cheers
 
No. I tried the same thing. Called AB and said the only thing you can do is use USB to flash and configure it. You can buy an inverter that will convert 120vac to 480 3 phase.
 
Be aware that the USB interface will not allow you to PROGRAM the drive, you WRITE the program off-line, then the USB port allows you to LOAD that program into the drive.

If you want to program it on-the-fly but without running it, you can also just get a basic control power transformer and feed it backward from your 230V single phase supply to give you a 400V single phase source and connect that 400V into 2 of the the drive terminals. It won't care if the input is single phase when there is no load on it. The usual precautions apply, i.e. don't forget that you now have 400V live terminals!

You can feed an exterior 24VDC supply into a PF750 drive (with an accessory card), but you give up that capability when you go with a Compnent Class drive like the 525.
 
I was under the impession that you could remove the front control unit from the power base and plug in a std usb cable to your laptop and program it, with the control unit getting it's supply from the usb port.
there is a sales video on youtube somewhere but I can't remember the link.

Steve

here we go.
https://www.youtube.com/watch?v=3nVgW5fEb4s
 
Last edited:

Similar Topics

I seem to be on here often lately but cant find specifics about my situation I am trying to control the drive using both ethernet and analog(for...
Replies
1
Views
747
When E300 powered off, the ethernet device tag data stayed at last know state, for example, fault bit is still Off, ready bit is still ON, status...
Replies
8
Views
1,006
Hello all, New to this site - I am adding a new conveyor and using a powerflex 525, though the rest of the drives operating this line are...
Replies
7
Views
1,281
I have a (*) PowerFlex 525 being supplied with 400VAC, 60 cycle, 3-phase. This is not a type-o, this is accurate. Now, the drive clearly states...
Replies
3
Views
1,178
Has anyone had any success using a PanelView Plus to directly control a PF525 over ethernet, I tried to use the file provided with TechNote...
Replies
1
Views
1,059
Back
Top Bottom