Spare ML1400

Tom@Pton

Member
Join Date
Dec 2009
Location
Central Nebraska
Posts
159
One of my customers wants a spare to his ML1400. Is there a trick I need to know about programming this spare? It will not have any of the other I/O installed until after it is in place. If and when it is ever needed.

When I downloaded the file it immediately, or soon after, faulted.
 
In general, MicroLogix and SLC-500 controllers will immediately fault when commanded to do into RUN mode if you don't have the I/O modules that are defined in the user program actually connected to the controller.

This is on purpose; if the controller doesn't have the input or output devices the control program needs, it's not going to try to run a user program or control outputs. It has no way of knowing if the missing I/O are important or unimportant.

SLCs let you inhibit I/O modules and go into RUN mode with missing ones, but I've never tried to do so with MicroLogix 1400.
 
In general, MicroLogix and SLC-500 controllers will immediately fault when commanded to do into RUN mode if you don't have the I/O modules that are defined in the user program actually connected to the controller.

This is on purpose; if the controller doesn't have the input or output devices the control program needs, it's not going to try to run a user program or control outputs. It has no way of knowing if the missing I/O are important or unimportant.

SLCs let you inhibit I/O modules and go into RUN mode with missing ones, but I've never tried to do so with MicroLogix 1400.

I suspected I should have left it in the program mode.
 
If you leave it in program mode, it will still be in program mode next time you apply power. Putting it in run mode means that it will try to go to run mode next time power is applied. With the right I/O modules, I think that is what you want.
 
I would buy and install the 1762 cards that you need, so that it is setup the same as your field unit.
Then, hopefully it will not fault.
Good Luck!
 
I’m guessing the reason for having a spare PLC is so that if it fails there will be very little down time. With that, what if one of the I/O modules fails? If they want spares, they should have spares of everything (within reason) that might fail and cause a delay in the system running.
 
I’m guessing the reason for having a spare PLC is so that if it fails there will be very little down time. With that, what if one of the I/O modules fails? If they want spares, they should have spares of everything (within reason) that might fail and cause a delay in the system running.

Yes, no doubt the best plan.

Thanks again to all.
 

Similar Topics

Scenario: client has a non-redundant L81E controller with one Ethernet connected remote chassis. Several spare slots are available. By contract...
Replies
2
Views
770
Does anyone have a spare PacDrive part# LMC600CBD10000? Not necessarily for sale, but to do a bench test. I have a CF image file, and I'd like...
Replies
2
Views
1,260
Hello, I've had a 1746-NT8 thermocouple input card fail on an SLC5/05 unit. There is another TC card in this rack that has spare input channels...
Replies
4
Views
1,636
Hi all, I have attached a list of PLC components that I have available. Most items are free but I can't cover postage. Send me a PM on any items...
Replies
7
Views
1,667
A question for the people who work on industrial sites. A customer complained about having to revamp several premium PLC that worked fine...
Replies
21
Views
8,046
Back
Top Bottom