Panelview plus

russrmartin

Member
Join Date
Aug 2002
Location
Eastman, Wisconsin
Posts
744
I have an application that I am trying to run in a panelview plus 700. When I load the application and run it, it goes to a blank white screen. Under the startup options in the menu tree the only thing checked is the initial graphic box, and I have my main screen in the space provided. Can anyone tell me why my screen would not be loading when I run the application? I am learing as I play with this thing, and I'm stuck as to what else I can check. Thanks in advance.

Russ

This is a 2711p series A terminal.
 
blah blah

Found out what my problem is, if there is anyone out there trying to figure out what I was doing wrong. After I had set up the screen I wanted to start out with under the startup tab, I did not create a runtime file. Did that now and everything looks good. Just a note for future learners.

russ
 
Be sure to configure a 'shutdown' button on an accessible screen!
If you set the PV plus to auto execute a screen on 'startup', then there is no way out....
I didn't have this problem....but it wouldn't be hard to find your self there :)
 
thanks

thanks for the tip. I already had this done, but only because I read it in the manual while I was looking for a possible reason to my other problem. Right now I am trying to figure out how I can import tags from a PLC5. When I browse tags, I can get to the word level from the online folder, but I cannot get to the bit level. Any ideas?
 
With the SLC 500 you can only browse to the word level. You have to manually enter the bit. I would imagine the PLC 5 would be the same.
 
Have you tried testing the application on your PC before downloading? See if it does the same thing there. My guess is that it is not loading your initial screen.

Try Application - Test Application to run it on your PC.

As far as it not loading, I have done this several times. Remember to create the Runtime and then download. I frequently will make a change and then download only to download the last (old) version because I didn't create the Runtime first.

Good Luck!!
OG
 
Be sure to configure a 'shutdown' button on an accessible screen!
If you set the PV plus to auto execute a screen on 'startup', then there is no way out....
You can cycle power and tap on the touch screen during the power-up sequence to get to the config menus.
 

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
76
Hi Everyone, Currently we have three plants running with Controllogix PLCs (L72, L73, L74). In each of these plants we have 2 FTView SE...
Replies
0
Views
52
Hello All! Ok, we got a Work cell from a Integrator that is sending saved scanning data from the PLC to HMI (Panel View Plus) when I look at this...
Replies
3
Views
77
Hello everyone. This is more of an HMI issue. I have a new PanelView Plus 7 Series B. I am using the alarm list object to display the fault...
Replies
0
Views
89
Hello, I made a change in alarm setup in factory view studio, where I changed a alarm message text. After that I made a run application and...
Replies
0
Views
129
Back
Top Bottom