Hello all,

I am trying to configure a 1794-AENT/A Firmware Rev 2.012 to run on a CompactLogix L24ER-QBFC1B controller. I have the flex module set up in the controller organizer tree. My issue is the module faults out on a (code: 16#0203) connection timed out, every 10 sec. The flex module recovers and then is fine for 10 secs and it does this over and over. The yellow alert signal shows up with the same frequency in the controller organizer tree, no surprise there, as well as the network status light on the flex module lights up red again no surprise there. I have tried configuring it on another PLC,multiple Ethernet cable, I have tried uni-cast, multi-cast, I have tried changing the RPI rate to both ends of the spectrum. I only each the one Ethernet Flex module to test with.
My questions are is there a certain minimum firmware that i need to use as an AOP?Does my configuration make scene?Has anyone come across this issue?

Thanks,

Lucas
 
First check to be sure there are no duplicate IP addresses on the network.

I know I've had to upgrade a bunch of POINT I/O adapters when we moved to the newest CompactLogix platform because of similar connection incompatibilities.

RA Knowledgebase article 509707 says that any CompactLogix 5370 family controller will exhibit a similar connection failure with 1794-AENT 2.1 or 3.1 firmware, and that 1794-AENT version 4.1 firmware will work with those controllers.
 
Thanks Ken
I was thinking it was firmware but wasn't sure
Do you know off hand what the series A are compatible with or can you point me to a doc that outlines that?
-Lucas
 

Similar Topics

I'm sure this question has been posted a thousand times on here but for me it was even funnier when I got to ask Rockwell / AB directly. My...
Replies
5
Views
164
Looking to see if there is any sort of publication or details on if I can tie a 1794 AENT module to a 3rd party eth/ip scanner (happens to be opto...
Replies
2
Views
703
I'm new to Flex I/O. Our company bought a used packaging machine that uses Flex I/O and we are trying to recommission it. I'm trying to establish...
Replies
4
Views
1,836
Good Afternoon , I have used many 1794-AENT Ethernet Adaptors , and never had this problem . I used BootP and assigned the IP Address , sent...
Replies
1
Views
1,883
Hi all, I've been working on a few Flex IO modules lately. I am setting up a second one with an IP. Here's what I've been experiencing: 1...
Replies
9
Views
2,393
Back
Top Bottom