DHRIO not communicating

JoelV

Lifetime Supporting Member
Join Date
Apr 2015
Location
Jackson
Posts
15
We have a DHRIO module that is only using the remote I/O

to talk to (4) Hardy scale systems. Yesterday one of the

maintenance technicians turned the power off to one of the

scales and after powering back up the scale would not

communicate through the DHRIO module. The other nodes on the

network communicated fine, but the resolution was to unplug

the RIO cable from the card then re-connect. we tried powering

down the processor and toggling from run to program beforehand

but they didn't work. Has anyone ever had a similar issue.

The module didn't show any faults but after removing the plug

the scale started reading and so far no more problems.


Thanks in advance
 
That sounds like a situation in which the scale needed to receive a BTW for configuration prior to responding to the BTRs that receive data from the scales. Either that, or a fault on the BTR stopped the logic that should be triggering repetitive reads from the scale.

I would look at the logic for both the BTW and BTR associated with the scales. If you replicate the problem while monitoring this logic online, then you should be able to see where the problem lies.
 

Similar Topics

hello, I have a problem with my AN-X2-AB-DHRIO Prosoft module, I can't connect with the module because I lost a microSD card that has firmware and...
Replies
12
Views
386
We have a remove PLC rack that is being used to collect data from older equipment via a 1756-DHRIO module. This module occasionally faults out...
Replies
1
Views
414
I have a 1756-L81e v32 using a DHRIO v7.001 in RIO scanner Driving (7) 1771 ASB Modules @ 115k baud. The Racks RPI are set at 48msecs. This system...
Replies
2
Views
902
Hey guys, We recently picked up a new customer that just finished a controls upgrade with some other systems integrator company. They upgraded to...
Replies
4
Views
1,759
I am trying to send some datas from PLC-5 to control logix plc through 1756-DHRIO. When I go online to PLC-5, Message instruction gives error &...
Replies
15
Views
3,372
Back
Top Bottom