I have an Omron CQM1H PLC that keeps having a reoccurring error. In CX Programmer I read the error as "FATAL I/O". I usually just power it down and unseat and reseat all of the cards and the error will clear. Any suggestions on how I can get this issue to quit or find the specific culprit without replacing the PLC piece by piece?
 
That fault indicates a problem with one of the connectors between the I/O modules. If the modules are not properly locked together vibration will cause the connectors to work loose.
If all of the module locks are properly in place and you have end barriers installed on the DIN rail then you really don't have any option except replacing the I/O modules one at a time.
 
Issues with connectors/backplane. The PLC is old and no longer supported. Replace it with a CJ2M - CX-P will convert the program for you. You may have to do a little manipulation of the code but it does it pretty well.
 
Fatal I/O Error

This is what I was afraid of. I'll try to replace the output cards first. My recommendation to management will be a CJ2 and a complete overhaul of the electrical in the near future.
Scary part of all of this is, we must have dozens of CQM1s, CQM1Hs and C60Ks currently running in our facility.
Job Security!! LOL
Thanks for the input.
 

Similar Topics

Hello to all We had an Over voltage power and 3 expansion cards connected to the plc were broken; and the plc showed the fatal error(POWER led is...
Replies
13
Views
9,260
Hi Everyone, I have a customer that needs a CQM1H (CPU51) replaced. They purchased the processor new-old-stock from a source they found online...
Replies
3
Views
337
I have an Omron CQM1H-CPU21 and a NS8-TV00B-V1, I have followed the manufacturer's spec on how to set this up and all I got is the HMI is trying...
Replies
7
Views
869
Hello maybe someone can help me, I have omron CQM1H PLC with CLK21 (Controller link module) and SCB41 (Serial module connected with NMB CSD-891B...
Replies
1
Views
537
Hi, I have an Omron PLC (CQM1H-61CPU) connected to an Omron HMI (NT631C). In order to connect a PC to them, I want to know: 1- Is the cable...
Replies
1
Views
848
Back
Top Bottom