Many thanks to everyone who shared thoughts on this!
What is the error message on your vfd.
The problem is - there is no error message, VFD is running the motor on very low RPM at maxed out AMPs:
(image does not want to load, here is the link to it:
http://postimg.org/image/syqyt6hgb/)
I would first start by powering down the panel, wait for the VFD DC Bus to bleed off to a safe (near zero) voltage, disconnect the motor and "ohm it out".
Thank you, I will "ohm out" the motor during this upcoming weekend and will share the results here.
...it sounds like the VFD is trying to run the motor and not faulting. If the 24 amps is above the motor FLA, and the VFD is programmed correctly, the drive should fault, given enough time.
Yes, VFD is not faulting, but I did not give it enough time. I think the longest I have ran it (since the issue appeared) was for 2, maybe 3 minutes. However, 24 amps is within the
motor FLA (click to see the FLA), so I guess running it for longer will not cause VFD to fault, but I can try to do this if needed.
Unfortunately it is not easy to check if motor/pump is clogged, but if control panel says it is rotating at 40 RPM, I tend to think this rules out the clogged motor.
If this assumption is wrong, I think I could take the motor off and check if it can rotate freely.
Unlikely. It is probably a centrifugal pump, so no flow = no load.
Unlikely. It is probably a centrifugal pump, so no flow = no load.
It might more likely be a BROKEN pipe and you have what's called "open channel" flow (no restriction), which might make the drive go into current limit mode, which causes it to reduce the speed in order to reduce the load on the drive.
Interesting, so if I will disconnect the motor from the pump and will try to rotate it without load, should I expect it to rotate at maxed out amps and low RPM (due to no load)? This sounds strange, I would rather expect motor to rotate fast at low amps.
If so, you might have current flowing to ground that the VFD is NOT detecting (because it has no ground reference). This would be a VERY VERY dangerous situation!!!
I will check the grounding. Is there any way I could check if current if flowing to ground (apart from touching it
)
Under the right (wrong) circumstances if the memory of the VFD was damaged or corrupted during power fluctuations, it may no longer have the right programming and is running on some sort of factory default values.
If I wanted to check the programming, where should I start? VFD manual?
I have no experience with VFDs, but I would say I am tech savvy.
5) Your pump has a bad bearing or some other mechanical problem which is increasing the load on the motor, causing the current limit / speed reduction response from the VFD as mentioned above.
This motor was installed only couple of years ago and was used lightly, besides, there is no loud noise when it is running at 40 RPM... so probably failed bearing is not the case.
5) 6) You have lost a phase on the incoming supply, which artificially limits the VFD's capacity, so it is again, lowering the load by reducing the speed to reduce the strain on the power components of the VFD..
Thanks, I will check that, but I would think VFD control panel would be able to recognize this fault.