AB PLC with batter operated

mbreddy

Member
Join Date
Nov 2014
Location
bangalore
Posts
22
Hi All,

Could you please let me know if any AB or any other PLC which operates with Battery and no external power supply?

Thanks,
 
Any PLC can be operated from a battery. If it's a 12 or 24VDC PLC, just hook up the batteries directly. If it's 120 or 240, use an inverter. You need to specify your actual requirements.
 
Any PLC can be operated from a battery. If it's a 12 or 24VDC PLC, just hook up the batteries directly. If it's 120 or 240, use an inverter. You need to specify your actual requirements.

Since you require Ethernet, do you have an HMI (or a PC with an HMI on it) that will also have to powered by the battery or inverter? What about a switch or router?

The more things connected to the battery will reduce the battery run-time, unless you're planning on a large bank of batteries to run the system.
 
Ah, when I read the title, I was excited about the prospect of a pancake-powered PLC. I'm so disappointed...
 
Aabeck said:
...The more things connected to the battery will reduce the battery run-time, unless you're planning on a large bank of batteries to run the system.

That's why battery run controllers, especially mini PLCs like the Barth, are designed specifically for battery supply. They are miniature and low power consumption devices, but this does tend to limit their capabilities.

rdrast said:
Any PLC can be operated from a battery...

Yes, powering a standard 12/24VDC PLC off a battery supply is doable, but is it power consumption efficient? As said, the battery pack will tend to be larger, as standard PLCs will have extra comms and peripherals pulling on the supply, perhaps negating the compact advantage of using the particular battery powered PLC?

But if size "doesn't matter", then by all means, hook whatever you need up to power them.

I'm asking more than telling. I'd be interested in hearing from anyone who has done this with a standard PLC?
I'm sure that sometimes, in some places, having a supply is a luxury.

G.
 
O/P give some more info as to the application...

If you need Ethernet I'd use a 24VDC Micro Logix 1100 and size a battery accordingly to how long you need it to run for.
 

Similar Topics

Apologies for not being the best IDEC programmer. I recently was doing some inspections on a site that had 3 FC6A IDEC processors. The issue is...
Replies
0
Views
31
"Hello! Good day! Excuse me, I have a question regarding the 1761-NET-ENI. RSLinx has already detected it but it's not connecting to the PLC...
Replies
4
Views
57
How to fix if appears code “$115 plc-restart running” on the screen OP17
Replies
2
Views
82
Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
20
Views
188
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
56
Back
Top Bottom