Analog output Siemens S7-300 series

Ljohansen

Member
Join Date
May 2015
Location
Odense
Posts
6
Hi

Quick question. Is there 4mA at the output on the analog card when it is configured in the HW and the card has 24VDC? Or does the output have to configured in the programming first?

Kind regards

Lasse Johansen
 
The card has to be set up as such in the hardware. It can be 0..20 mA or 4..20mA or a voltage signal.

Maybe you could elaborate a little bit?
 
If no value is written to the card in the user program, then the card will output what corresponds to 0 (zero).
That is 0 mA for a card configured for 0-20mA, and 4 mA for a card configured for 4-20mA.
 