Hi Guys!


I have a problem with re-enable PowerFlex 525 after fault.

I've connected the safety 24V of the inverter 525(S1 and S2) through the safety relay.
When I hit the E_stop I'm loosing 24V on the safety side and the inverters goes faulty.(Fault 059)
I set up the Automatic Reset parameter A541 to value diffrent than 0(says manual),,,so i put insted 1.
but still does't reseting itself.
Only when I will press stop command on the keyboard it's reseting.
I'm not driving the inverter by Ethernet.

If anyone have any ideas, please don't hesitate to contact me.
It's very urgent situation!!!!!!

Thanks a lot!!!!!
Michael
 
Is your Run Signal to the 525 VFD still on. Most VFDs, including AB VFDs will not Reset until VFD is taken out of Run. This may be what you are doing when you push the Stop Button on the VFD.

Stu....
 
Hi

Hi

I think the run signal was not necessarily on because I'm using this inverter to run the infeed table.
Sequence looks like:
Move forward 6 seconds then waiting 2 seconds then going backwards 1,5 s and then wait next 10 seconds before it starts moving forward again.

So I think even the drive was waiting this 10 second during the waiting period
(so during this 10s I'm not sending any command from PLC to the drive)
and at the same time when I hit the E_stop,,,,the drive became faulty and didn't reset itself.

Any more ideas?

Many Thanks
 
HI
I have had exactly the same issue. when Safe Off loses 24vdc default is to hard fault drive. Reset Parameter 105 "Safety Open EN" to FaultDisable. Safe Off will still work. I always test A) to make sure it does disable B) that it does not fault.

Rich
 
Hi Rich!

So what should I do exactly?
Set the Parameter 105 "Safety Open EN" to FaultDisable,,,it's that right?
If this will solve the problem?

Thanks a lot
 
yes set P105 to FaultDisable. A&B are simply suggesting that you test first to make sure when you remove 24vdc from safe off terminals that drive intiates a safe off disable/stops. Next confirm that when it stops it does not Fault the drive and auto-resets when you re-power Safe Off Terminals.

Test Always Test Everything during commissioning is my MOTTO.
Cannot test too much.
Rich
 
Hi All!

Thanks for your advices guys.

It was really helpful, when I set up this parameter t105 everything comes to normal
as it suppose to be.

Mike
 

Similar Topics

Can you configure a Powerflex 700VC Drive to run without a hardwired "Enable" circuit? The drive is connected to the PLC through ethernet and I...
Replies
4
Views
1,890
Hello I have In touch 10.1 I tried to enter the WindowMaker to make some adjustments I am using a dongol for the license . I can access the...
Replies
1
Views
86
I'm using one TON (called SystemTimer) throughout a program that I change the .PRE given different conditions. I'm porting an IDEC ladder over to...
Replies
8
Views
313
Hello Friends I have a installation with v16, v17, v18, v19, v20. When I tried to open a v20 file, the enable source protection was not enabled...
Replies
1
Views
236
Hi there, Maybe I am overthinking this issue, but here is what I have going on. I have a program running for a water valve on a DI system. We...
Replies
4
Views
449
Back
Top Bottom