Hi Everyone,
I am currently reverse engineering a hydraulic unit with a CompactLogix L35E and I have an issue with a Differential Pressure transmitter as I need to scale the analog input in the PLC. I am a long time user of AB software however the scaling I'm trying to achieve with the analog has me stumped, the transmitter is not a smart or hart compatible, therefore I need to do the scaling within the PLC.
Ok this is the situation.
1. Diff Pressure Transmitter 0-5000psi
2. Re-scaled range in PLC 255-3000psi
3. Then convert the above into 0-100% (255-3000psi)
I have set the AI channel configuration as,
- 4mA to 20mA
- 50Hz
- Engineering Units
I have also created a CPT instruction to scale the 4-20mA with the equation (DPT1-4000)/16
If anyone can provide some assistance, it would be much appreciated.
Thanks in advance
James
 
Sorry guys, I missed some significant key points;

1. Diff Pressure Transmitter 0-5000psi
2. Used range in PLC 255-3000psi
3. Then convert the above into 0-100% (255-3000psi), as this diff pressure is represented as torque 0-100% for operations.

mA​
Psi​
Percentage​
4​
0​
4.816
255
0
14
3125
100
20​
5000​

Unfortunately because I am using a 1769-IF4, I don’t have the ability to manipulate the AI channel configuration as per a 1756-IF8.

Thanks
James
 
Use a real for the analog input engineering unit

0 psi = 4 mA.......5000 psi = 20 mA .....Difference = 16 mA

From the engineering unit real subtract 4 to give you the scaled input scaled across 16 mA
use a real for this result

5000 divided by 16mA =312.5 per mA

Get the scaled input real and multiply it by 312.5 to give you your wanted Psi real value

The difference in your Psi scaling is 3000 minus 255 = 2745 for your % answer
Get the Psi real and subtract 255 to get a differential real for your % answer

Now all you need to do is

100 multiplied by the differential real for your % answer divided by 2745

There are many ways you could set this out to get your result
but this gets you what you have described
 

Similar Topics

from an email: this is a fairly common question - and since I'm swamped with other projects right now, I've decided to post my answer to...
Replies
7
Views
5,893
I need some programming help with bringing an Analog Input (4-20mA) into a Control Logix Processor via analog input module(1794-IE8). I'm tring...
Replies
5
Views
8,939
I'm trying to think of a logical way to clamp a group of 32 analog inputs so that if they ever go out of range, the program will clamp them at...
Replies
12
Views
3,358
hi folks! here i am with my debut in this forum. I am using Rslogix 5000 ver17.2,have a fast analog module(1769IF4XOF2F)to be added to my project...
Replies
5
Views
3,976
Hi! So my problem is a little funky, I had Studio 5000 v 24 and 30 installed, but forgot to install RSLogix (which I cannot go without). Is there...
Replies
2
Views
112
Back
Top Bottom