Hi Everyone,
I am currently reverse engineering a hydraulic unit with a CompactLogix L35E and I have an issue with a Differential Pressure transmitter as I need to scale the analog input in the PLC. I am a long time user of AB software however the scaling I'm trying to achieve with the analog has me stumped, the transmitter is not a smart or hart compatible, therefore I need to do the scaling within the PLC.
Ok this is the situation.
1. Diff Pressure Transmitter 0-5000psi
2. Re-scaled range in PLC 255-3000psi
3. Then convert the above into 0-100% (255-3000psi)
I have set the AI channel configuration as,
- 4mA to 20mA
- 50Hz
- Engineering Units
I have also created a CPT instruction to scale the 4-20mA with the equation (DPT1-4000)/16
If anyone can provide some assistance, it would be much appreciated.
Thanks in advance
James
I am currently reverse engineering a hydraulic unit with a CompactLogix L35E and I have an issue with a Differential Pressure transmitter as I need to scale the analog input in the PLC. I am a long time user of AB software however the scaling I'm trying to achieve with the analog has me stumped, the transmitter is not a smart or hart compatible, therefore I need to do the scaling within the PLC.
Ok this is the situation.
1. Diff Pressure Transmitter 0-5000psi
2. Re-scaled range in PLC 255-3000psi
3. Then convert the above into 0-100% (255-3000psi)
I have set the AI channel configuration as,
- 4mA to 20mA
- 50Hz
- Engineering Units
I have also created a CPT instruction to scale the 4-20mA with the equation (DPT1-4000)/16
If anyone can provide some assistance, it would be much appreciated.
Thanks in advance
James