S7-400 redundant seperate

Join Date
Nov 2014
Location
ulaanbaatar
Posts
10
Helloo. everyone. i want ask something about s7-400 redundant mode THAT
Our industry got s7-400 redundant PLCs(2 plc works by redundant).

i suppose to seperate 1 plc and to cancel redundant mode from our redundant system. so i want to our plc works by standart (1 plc works as indepedently)
then i dont know what hardware & software trouble will happen?
what should i do?
 
If your PLC pair is working correctly, then you should be able to take one away and still have it function correctly.

However, depending on how it was implemented, there may be a large amount of reconfiguration required to make all the red error lights go away.
 
yeap
1. Firstly disconnect optic cable between 2 plc
2. seperate ET module's probi cable
3. then change hardware configuration on software.
any other things need?
 

Similar Topics

Hello, I have a customer that requests Redundant IO for S7-400. I have only found solutions with ET200M modules. Is it not possible to configure...
Replies
3
Views
1,728
Hello, The only option for redundant connection from two redundant WinCC PCs to a S7-400H system is industrial Ethernet and Redconnect software...
Replies
0
Views
1,789
Hi, I want to connect a non-redundant profibus network to a redundant Siemens S7 400 H system. Because of the data capacity the y-link isn't...
Replies
1
Views
8,687
Any one can help me how to configure the redundant system of S700-400 CPU 416 and 10 unit of ET200M run via profibus. Thank you. Ali
Replies
1
Views
3,991
Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
27
Back
Top Bottom