Customer installed two SMC Flex soft starters to replace Dialog Plus units that died.
They have everything set up correctly on one of them and the other is locked out awaiting a motor replacement.
Unit 1 is Rack 3, group 0, 1/4 rack and is apparently talking to the CPU just fine.
Unit 2 is Rack 3, group 2, 1/4 rack and powered down. There are no more devices on this logical rack.
Unit 1 shows no faults on the HIM, and I can run it in Hand (selector switch to the terminal strip) or from the Keypad.
I have tried all possible wiring options and parameter changes in the book and some not in the book, and I cannot get this thing to run via RIO control.
I always have bits 7, 8, and 9 coming in to the RIO input word 0. Bit 7 is the Fault bit according to my book and I forget what the others mean. I never see the enabled bit turn on. None of these bits ever change states unless I inhibit the module in RSLogix 5000and zero them myself.
There are no faults on the HIM for the 20-COMM-R or the Flex SMC. I can make it fault by changing parameters and then the HIM will flash the Network Loss fault, but those three bits coming back over the RIO network are the only three I ever see and they never change.
I have power cycled the whole system, power cycled just the SMC multiple times and I am stumped. I disabled the rungs controlling the output bits that should control the stop and start inputs to the starter and toggled them manually in every possible conceivable order and pattern and I have gotten no response.
The HIM shows "Stopped". The HIM and the DPI port 5 are both masked in. Matter of fact, I turned on all the logic mask bits to no avail.
There is a remote HIM mounted on the enclosure door. There is a HIM built into the starter, and then there is also the 20-COMM-R, in case there is a limit to the number of DPI devices.
I am going back to the site after lunch and use their Techconnect to phone a friend, but I am not optimistic on this one. I do not believe they have any spare parts, but I may try to see if I can control the state of one of the Flex outputs and wire it to the bypass contactor. This application should be fine running DOL, but I want to get to the bottom of this mystery today if possible.
If anyone has seen this before or has any ideas for me, I would be grateful.
Paul
They have everything set up correctly on one of them and the other is locked out awaiting a motor replacement.
Unit 1 is Rack 3, group 0, 1/4 rack and is apparently talking to the CPU just fine.
Unit 2 is Rack 3, group 2, 1/4 rack and powered down. There are no more devices on this logical rack.
Unit 1 shows no faults on the HIM, and I can run it in Hand (selector switch to the terminal strip) or from the Keypad.
I have tried all possible wiring options and parameter changes in the book and some not in the book, and I cannot get this thing to run via RIO control.
I always have bits 7, 8, and 9 coming in to the RIO input word 0. Bit 7 is the Fault bit according to my book and I forget what the others mean. I never see the enabled bit turn on. None of these bits ever change states unless I inhibit the module in RSLogix 5000and zero them myself.
There are no faults on the HIM for the 20-COMM-R or the Flex SMC. I can make it fault by changing parameters and then the HIM will flash the Network Loss fault, but those three bits coming back over the RIO network are the only three I ever see and they never change.
I have power cycled the whole system, power cycled just the SMC multiple times and I am stumped. I disabled the rungs controlling the output bits that should control the stop and start inputs to the starter and toggled them manually in every possible conceivable order and pattern and I have gotten no response.
The HIM shows "Stopped". The HIM and the DPI port 5 are both masked in. Matter of fact, I turned on all the logic mask bits to no avail.
There is a remote HIM mounted on the enclosure door. There is a HIM built into the starter, and then there is also the 20-COMM-R, in case there is a limit to the number of DPI devices.
I am going back to the site after lunch and use their Techconnect to phone a friend, but I am not optimistic on this one. I do not believe they have any spare parts, but I may try to see if I can control the state of one of the Flex outputs and wire it to the bypass contactor. This application should be fine running DOL, but I want to get to the bottom of this mystery today if possible.
If anyone has seen this before or has any ideas for me, I would be grateful.