hi . we are using beckhoff decentralised I/O module on profibus , which has its different analog cards for RTD , current and Voltage input. i need to get an 4mA-20mA input , though we had only 1 channel current input card so my supervisor gave me a 2 channel analog input card but its RTD input type. Is it safe to safe that i can't use the RTD analog input card for current measurements or i need to go through the manuals again.

2. in new TIA portal v13 i have noticed that the analog scaling blocks are a little different now. the NORM block has the input high and low range as well as the output high and low range . does that mean we don't have the to use the scaling box to scale input 0 to 1 to use NORM block to scale to physical range.

any help would be highly appreciated thanks ..
 
Is it safe to safe that i can't use the RTD analog input card for current measurements

You can not use an RTD input card for a 4-20mA signal for any brand or model.

An RTD input card sources a constant current (typically less than 1mA) and reads the voltage drop across the RTD resistance.

A 4-20mA current source is not compatible with the actions going on in an RTD card.

With regard to question 2 scaling, I have no idea.
 
The older scale and unscale blocks are still there, you just have to look for them. There should be a menu/folder somewhere near the norm and new scale instruction blocks where you can find the older blocks to use in your program. If you can't find them, I can look at my laptop with TIA on mon.
 
yea , i just need to scale an input giving input low/high and output low/high variables. so if the new norm block just does the same thing its better . but i don't understand why is there also a scale block then.

maybe for backward compatibility?
 
What PLC are you using? I'm pretty sure I just used the old scale block less than a week ago with an S7-1500.
 
Here's a screenshot of the instructions window in a project using an S7-1500. Scale and Unscale are under the "Others" folder.
 
#1 with a relay it is possible to look at two 4-20 mA signals, slowly but it works.
it must be close before break, to avoid alamrs from the card.
what is the typenumber on the cards?
 

Similar Topics

Good Morning , I have a RTD , that I would like to wire into a 1756-IF8 Analog Input Card. Would you all a simple wiring diagram , of what...
Replies
4
Views
1,199
Good Afternoon , It seems like we always have problems with using Type J Thermocouples with our slip rings . Would using a RTD at 10...
Replies
6
Views
1,640
We are running a power flex 70 connected to a Delta V and I cannot get the drive to start because I am getting a STOP ASSERTD message on my HMI. I...
Replies
4
Views
3,028
I am working on an installation that will require sensor cabling interconnecting sensors to PLC subject to outdoor temperatures. Will the ambient...
Replies
3
Views
2,062
Hello! I have RTD sensor with 4 wire and shield ( 2 red wire + 2 white wire + Shield) and I want to connect to 1734-IR2 module. But in the manual...
Replies
2
Views
1,432
Back
Top Bottom