Now this...
PERSPOLIS said:
I have a question in regards to COMM0 led flashing rate on Micrologix 1500 communicating with PV plus6 400 {DF-1 protocol}. Should the flashing be fast or slow or it should not matter as long COMM0 led is flashing...
...Under the same setup when PV 300 connected to Mlogix 1500 then COMM0 led flashes very fast similarly when PV plus 6 400 is replaced with PV 300 under the same communication configuration then COMM0 flashes very slow...
Good question.
Communications difference...
PanelView Plus running FactoryTalk View ME application
...Verses...
PanelView Standard running PanelBuilder32 application
With the communications cable plugged in, and successfully communicating, the COMM 0 LED will flash intermittently as data packets are being transmitted. The rate at which it may flash will depend on the volume, speed and frequency at which it is transmitting data.
Depending on the application, such as that for a HMI using DF1, the volume of data could be a little, or a lot. The speed of the data transmission would be dependant on the baud rate and the distance between the devices over the physical network. The frequency of the data transmitted would be determined by the rate that tags are updated, or refreshed on the HMI, and which type of application is in use.
For ME applications, the tag data is refreshed per Display that is currently loaded, using a Tag Update Rate, which is configurable per Display. The default Tag Update Rate for each Display is 1 second. Each time a new Display is loaded, the tag data for the Display's objects are refreshed with the controller. Only these tags are currently on scan out of the entire Tag Database, so the COMM 0 LED may appear to blink somewhat slower.
For PB32 applications, tag data is updated per tag and all tags are refreshed at their individual Update Frequency rate, regardless of whether their objects are on task or not. In other words, all tags are resolved against the Tag Database at their specified Update rate, each and every time. This means that all tags for the entire Tag Database are frequently being scanned, refreshed, or updated. This would be indicated by the COMM 0 LED blinking faster than you observed for the same project under FTVME.
In PB32, the default Update rate for each tag is 1 second, but can be changed from 1 up to 9 seconds. The default view for the Tag Editor in PB32 does not display the "Update Frequency" column. To view and edit this you can enable the "Extended Attributes" columns. This is done by clicking the 6th icon from the right above the Tag Editor columns. Five extra columns are added to the right...
Scale
Offset
Minimum
Maximum
Update Frequency
The Update Frequency will display a value of 1 for all tags still at default.
This parameter can also be accessed per tag via the "Tag Form" window which is opened when you select "Edit Tag" via a graphical object's properties window.
-----------------------------------------------
Note: For SLC or MicroLogix controllers...
With the Channel 0 Port configured for the DF1 protocol:
If you plug out the communications cable the COMM 0 LED will be OFF.
This indicates the port is configured for DF1, or disabled.
With the Channel 0 Port configured for the DH-485 protocol:
If you plug out the communications cable the COMM 0 LED will flash approximately once per second. This is because the controller is announcing itself to the DH-485 network.
The above is useful to know if unsure and you are trying to determine which of these two protocols the port may be using.
Regards,
George