Does anyone know how to use a Red Lion DSPLE device to swap the word ordering in MODBUS holding register messages? I'm wanting to use this device in between a MODBUS master and slave to translate the big/little endian word formats between two standards.

I have the configuration software (Crimson 3) connected, but not sure if I should set up a gateway, or 2 different master/slave protocols. :confused:

Marty

redlion1.jpg
 
MODBUS word swap working OK.....

After spending some time on it, I got this working in case anyone needs something similar.....

Using Red Lion DSPLE000 to swap the word order from a MODBUS (over Ethernet) device that sends the high word first. Set up master and slave protocol as shown in the pic below. In the slave protocol, added a block of registers and mapped LONG blocks from the master registers to slave by dragging the right register type from the master side. Then, selected Word Ordering: Low Then High.

One other problem that had to be resolved was to set the master protocol, PM1, option: Ping Holding Register to 0 to prevent communication problems between the DSP and the MODBUS device.

The result was to convert data words from this: 1234 5678 to this: 5678 1234.

This Red Lion device will convert many different protocols and is very flexible with specific register mapping, etc. This is one example of its capability.

Marty.

RedLionDSP.jpg
 
Last edited:

Similar Topics

Hello everyone I'm curious if I can create a register in the Red Lion DSPLE. What I'm trying to do is send some data via my ControlLogix to...
Replies
4
Views
1,652
Hi All, I'm a newbie to the forums here and to PLCs in general. I am working on a project where I want to use a Red Lion DSPLE to do protocol...
Replies
0
Views
1,190
I have a DSPLE that has a tag set up to add two values. The equation is If (tag1!=tag2) tag2:=abs (tag1+0); Yet the value of tag 2, when...
Replies
11
Views
3,176
Hello All, I'm investigating a Red Lion DSPLE setup that facilitates communication between an Allen Bradley PLC (ethernet) and CNC controller...
Replies
0
Views
2,462
Hey guys, I am trying to make an Allen Bradley Compactlogix and a Modicon Quantum talk to each other using a Red Lion Data Station. So far I've...
Replies
2
Views
2,997
Back
Top Bottom