briesejl5378 Member B Join Date Jul 2015 Location Athen, AL Posts 2 Jul 17, 2015 #1 Hello all I am fairly new to the direct logic plc's is there a one shot contact for the DL240 CPU.
gclshortt Member Join Date Dec 2014 Location Ontario Posts 3,217 Jul 17, 2015 #2 https://www.automationdirect.com/static/specs/dl205instr.pdf In the Direct Logic PLC's this is referred to as a differential. Positive differential (PD) One-shot output coil. When the input logic produces an off to on transition, the output will energize for one CPU scan. Regards, Garry http://www.accautomation.ca
https://www.automationdirect.com/static/specs/dl205instr.pdf In the Direct Logic PLC's this is referred to as a differential. Positive differential (PD) One-shot output coil. When the input logic produces an off to on transition, the output will energize for one CPU scan. Regards, Garry http://www.accautomation.ca
briesejl5378 Member B Join Date Jul 2015 Location Athen, AL Posts 2 Jul 17, 2015 #3 Thank you that is what I found after a bunch of digging in the software and was able to use that as an input for a one shot to start my rung. thanks for the help
Thank you that is what I found after a bunch of digging in the software and was able to use that as an input for a one shot to start my rung. thanks for the help