Hello, I am still fairly new to this direct logic plc programming. I have gathered some information on the set up for some modbus tcp communication. I encountered a problem when i was converting the modbus addresses to the koyo plc tag. i have a 2 slave elements one with the modbus address 30001 and another with the address 40001. When i do the conversion they both have the v memory tag of 0. How do I distinguish between the two in the programming and tagging. Thank in advance for you help.
 
You didn't note the CPU. In the DL06 manual, chapter 4 (System Design and Configuration) - Network Master Operation view the note that shows how the upper nibble of the Byte Count can be set to '4' to use Function 4.
 
I'm sorry I misled you. From the ECOM manual page 5-15 - the ECOM100 (just ECOM is not capable of Modbus/TCP) as a Client (Master) does not support Function Code 4. The 30001 address ranges cannot be read from a server/slave device.

My earlier post only applied tot Modbus RTU.
 
If you were to change the CPU to a Do-more processor, it can handle the major MODBUS function codes and the H2-DM1E model has a built in Ethernet port. The coding and software is different than the DirectLogic D2-250-1 however.

The software is free and there are a lot of benefits to using the Do-more over the older DirectLogic CPU's such as strongly typed memory, no need to interlock communication instructions, more available protocols and a vastly superior instruction set.
 

Similar Topics

Hi, I have been trying to run drive via Sysmac studio. I can ping the drive. I can see the logic bits going on/off as per command. But, drive is...
Replies
20
Views
325
Hello Guys, I am using 1769-L36ERMS PLC by Rockwell which doesn't let me MOV or COP literal text into string datatype? i very well know the...
Replies
13
Views
321
Good Afternoon , Does Rockwell Automation have an Input Card , maybe in the 1734 series , or CompactLogix series that will receive signals...
Replies
15
Views
737
Hi, I am new here, also I am a beginner in PLC programming and connection. I have a project in which the programming are made for 5 plcs, the...
Replies
1
Views
263
Hi everyone, I'm working on a project that involves using a Keyence LR-X100 sensor in Studio 5000 V35 ladder logic to determine the object's...
Replies
4
Views
597
Back
Top Bottom