temp/humidity
I had quite a number of erratic problems with a temp/humidity sensor at a thing called the CoolZone. He had installed the system with a several thousand dollar greenhouse controller, to turn water mist nozzles on and off on hot days.
The maintenance chap who hired us told us it was a voltage output; we hooked it up to a Micrologix 1000 w. analog and calibrated it.
Several service calls later, to adjust s caling and offsets, he told us it was current output, then told us it was RTD.
I told him that he had been wasting our time with all these calls when he didn't even know what sensor 'twas, after he had been trashing our program and PLC and saying that he, and the end customer, were losing mney and getting irate at us.
We eventually climbed up on the roof and opened the sensor box to check for ourselves. We found the shiny new sensor wrapped in a yellow rubber sleeve tagged "Remove before installation". Arrgghhh!
We had the last laugh as we notified the end customer that his contractor had royalled f'dup, and wasted the greenhouse controller because the installer didn't do his job.
We ended up buying a industrial wall-mount thermostat, and just using it as a digital input to the PLC.
Bottom line:
- check that the sensor is right for the analog card - current vs. voltage, or ??
- check that the analog card is set up for the sensor - DIP switches, jumpers, initialization values in the O registers.
- try a hot/cold test on it, if your sensor is rated for it - dip it in ice water and check the output at 0C/100%RH, and then boiling water to check the output at 100C, or use some other known temperatures.
RT