I have 2 PID blocks running at the same time and they seem to be giving identical outputs and SV and PV are different on each. Any ideas why this is happening and what I could do to fix it.

Data:
PLC = Delta DVP 32EH2
Analog Module= DVP 06XA 4 in 2 out set on 4ma - 20ma.

Both PIDs run on the same parameters in registers D100 - D109

1st PID Information
SV = D2103
PV = D16
Output = D150

2nd PID Information:
SV = D2099
PV = D18
Output = D151

I have attached a screenshot showing the HLT heater running. It didn't start until the BK Heater cut on. The HLT was already above set point so heater shouldn't have been running. Any help solving this one would greatly appreciated. I kind of think this is something that started recently. I don't think this problem has been going on since I started testing.

Thanks,

David

Screenshot.jpg
 
First, I would ask why you think you need to "fix" these two PID loops? I'm not really familiar with Delta PLCs, but I find it odd that a program that has been operating normally would suddenly create a problem.

So what if the two PIDs are operating on the same configuration parameters? They may be for twin processes. Is it possible that they are different PIDs for a single process, and that there is logic in the program to select which loop is active under certain conditions?

A heater "starting" and running when it shouldn't run doesn't sound like a PID issue. If you have concerns regarding an interlock issue, then the PID controls might not be where the problem lies. Did you write these PID loops? Did they work properly until recently?
 
First, I would ask why you think you need to "fix" these two PID loops? I'm not really familiar with Delta PLCs, but I find it odd that a program that has been operating normally would suddenly create a problem.

So what if the two PIDs are operating on the same configuration parameters? They may be for twin processes. Is it possible that they are different PIDs for a single process, and that there is logic in the program to select which loop is active under certain conditions?

A heater "starting" and running when it shouldn't run doesn't sound like a PID issue. If you have concerns regarding an interlock issue, then the PID controls might not be where the problem lies. Did you write these PID loops? Did they work properly until recently?

I wrote the loops. This may have been going on all along as I have had a lot of bugs and logic issues throughout my first automation project. The problem may be the parameters are not able to be used by multiple PID. I'm reading something in the manual under the PID instruction that says: there is no limitation on times using PID instruction but the register # holding the parameters can't be repeated. Does that sound like I need to create a new set of parameters for each PID instruction?

Thanks,

David
 
I wrote the loops. This may have been going on all along as I have had a lot of bugs and logic issues throughout my first automation project. The problem may be the parameters are not able to be used by multiple PID. I'm reading something in the manual under the PID instruction that says: there is no limitation on times using PID instruction but the register # holding the parameters can't be repeated. Does that sound like I need to create a new set of parameters for each PID instruction?

Thanks,

David


Yes, it does.
 
First, I would ask why you think you need to "fix" these two PID loops? I'm not really familiar with Delta PLCs, but I find it odd that a program that has been operating normally would suddenly create a problem.

So what if the two PIDs are operating on the same configuration parameters? They may be for twin processes. Is it possible that they are different PIDs for a single process, and that there is logic in the program to select which loop is active under certain conditions?

A heater "starting" and running when it shouldn't run doesn't sound like a PID issue. If you have concerns regarding an interlock issue, then the PID controls might not be where the problem lies. Did you write these PID loops? Did they work properly until recently?

Yes, it does.
Do you think it would only apply if I'm running 2 different heaters at the same time or for every PID instruction?
 
Every PID instruction needs its own unique registers.
You can't just reuse them.

Thanks, was just conserving space and trying to keep it tidy. I have 11 PID instructions in the program and each take 20 registers. I have not tested it yet to make sure my problem is solved but will check it tonight.
 

Similar Topics

I don't have a lot of experience with the 90-30 PID, but I'm working on some for an existing system. My question concerns manual operation. It is...
Replies
18
Views
3,816
Hello, I've done several migrations from SLC 5/05's to 5370 L33ER Compactlogix controllers. I've just encountered my first PID instructions with...
Replies
2
Views
1,690
Hey all, I'm pretty new to PLC programming and am on a team doing a PLC5 to Studio5000 conversion. After doing the built in conversion, I've...
Replies
6
Views
2,522
I'm constantly amazed by the number of "things" that can be copy/pasted or just drag/dropped from one application to another but I think I may...
Replies
3
Views
1,408
Processor: Modicon Quantum 652 60 Software: Unity 7.0 Language: LL984 Equipment: Extractor (basically, a large drag conveyor) Input: Level...
Replies
9
Views
2,945
Back
Top Bottom