Hi guys:

I am trying to setup IP address for some point IO system with adapter model 1734-AENTR.

I connect the laptop with adapter directly. Set the thumbwheel to 999. Then start BOOTP/DHCP utility. I can then see the response from the adapter. I then double click and assign the IP to it. Then when I want to assign this configuration to the device by disable BOOTP/DHCP. BUT, when I click the button, I get a Communication Error message, saying "Failed to complete the requested operation..." See my attachment.
My laptop is window 7, and I have disabled the firewall.

Another strange thing is the adapter always has a flashing red light on Module Status LED. Not sure how to clear it and if it is related with the problem above.

Any idea?

2.jpg
 
Have you correctly configured the Subnet Mask for BOOTP/DHCP Server?

Go to Tools>Network Settings

Do you have a wireless network connection on this computer and if so is it disabled?

If your LAN connection is set to "Public" then try setting it to "Home" or "Work".

There a few reasons why the adapter's Module Status LED may be flashing Red, but as you are only at the IP address setting stage, it is most likely that it is just not configured correctly yet. I would get the static IP address assigned first and then tackle the Module Status.

From your screenshot, BOOTP/DHCP Server appears to be successfully assigning the adapter a DHCP (Dynamic) IP address, which you now need to set Static.

If you cannot disable BOOTP/DHCP via BOOTP Server, then you can also attempt to do so in RSLinx Classic using the currently assigned DHCP IP address. If you can browse to the adapter using and Ethernet driver, then you can right-click it and go to Module Configuration>Port Configuration and set it to Static.

You can also do the same as above in RSLogix 5000/Logix Designer under the I/O Configuration, if the adapter has been added.

If the DHCP IP address is not being successfully assigned by BOOTP/DHCP Server, then you would have to initially set the adapter to a known IP address (192.168.1.x) using the thumbwheel, and also assign your computer a unique IP address on the same Subnet (192.168.1.y), and then use RSLinx Classic or RSLogix 5000/Logix Designer.

Another option, once a known IP address has been assigned via the thumbwheel, is to use an Internet Browser to browse to the adapter's embedded HTML webpage. Here you can go to Configuration folder on the left and expand it [+].

Enter lowercase...

username: admin
password: password

Then go to Network and from here you can disable BOOTP/DHCP and assign your Static IP address.

Click Apply Changes

Hopefully something there will get you going.

P.s. If you do assign an IP address via the thumbwheel, don't forget to set it back to an invalid number when done (255 through 887, or 889 through 999).

Regards,
George
 
Last edited:
As usual, George's info is pretty thorough - the only thing I'd add to it is to disable your wi-fi adaptor while you're using BOOTP. That's given me that same issue before.

edit: whoops, nope, George covered that as well. Don't know why I thought he'd have missed something like that ;)
 
thank you all.
It finally works. It looks like it is because I have wrong config on network setting in BOOTP.

And when I disable BOOTP successfully, the red flash LED is gone as well.
 

Similar Topics

Hello all - Preface: This is my first time working with these modules and Studio5000. I have a 1734-AENT/C setup in slot order of 1-IB8S, 2-IB8S...
Replies
4
Views
4,164
I am trying to figure out a way to reset the count of this module on power-up back to what it was before the power cycle. The module resets to...
Replies
7
Views
7,357
Does anyone know how to do this via MSG or SSV? All I want is the "Reset Module" type of command that one can find in the third tab of the generic...
Replies
1
Views
2,326
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
245
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
87
Back
Top Bottom