GEC Micro 3 control system interfacing

Join Date
Aug 2015
Location
Gauteng
Posts
2
I hope there is someone that can assist in this problem or that have more extensive knowledge of interfacing to a GEC micro 3 control system. I have never done a similar program like this before.

Our objective: To interface to 6 ammonia compressors, 5 of them containing micro 3 control systems and 1 compressor is a G force control system which is a bit more advanced.
Equipment that is used: Delta DOP B series HMI with Ethernet capability, SS2 Delta plc.

For a quick test a basic communication program was done and with a few test registers tried to communicate with modbus 485 RTU to one compressor. A few registers was used on the HMI. We quickly noticed that nothing is happening on the network. During our testing we discovered that the GEC micro 3 have a test program and we also discovered it has a loop-back function test on the control panel of the micro 3. On this loop-back test the communication protocol is clearly indicated. We removed the temporary network and the loop-back was prepared directly at the control panel.

Results:
1. Loop-back is failing on the micro 3 control system of the ammonia compressor. We tried another compressor and this also failed. Software version of the micro 3 was checked and it is of the correct version with communication. Maybe we are making a stupid mistake somewhere but all efforts is now at a standstill.
2. We also noted that the communication LED on the micro 3 panel is not flashing at all. This is serious. Our thought pattern is that somehow the communication function is disabled or not enabled on the micro 3 control panel. Various emails were send but we cannot get the proper information neither the correct technician to speak to. We have no idea how to get this communication going on this micro 3 control panel. Maybe someone have the knowledge. Or is this a case where we will battle for months to get a GEC technician to do a 15 minute configuration on the compressors?

Any help will be appreciated.
 
You may need to clarify exactly what a "GEC micro 3" is. Google and I do not know.
 

Similar Topics

Hi all, this is the first time I have posted on here, I have been reading with interest for a few years now. The problem I have is regarding...
Replies
1
Views
1,513
I'm trying to communicate with a Markem Image printer trough this card but I'm not able to connect. I have configured the client IPserver with...
Replies
1
Views
1,562
Hello, We have an installation where we use CLX controllers and now we want to implement a printer that receives his ASCII commands out of our...
Replies
8
Views
3,126
Well, as my tile suggests... is there anyone out there still using GEC/CEGELEC GEM 80 PLC's? If so, any sources of spares, either second-hand or...
Replies
2
Views
5,803
Hi,I need some help...this is my first time using vijeo Citect Scada.I need to collect data from allen bradley PLC SLC 500 which using MVI46-GEC...
Replies
0
Views
4,224
Back
Top Bottom