Hi
I need your help
I want know that how many stations(wincc,op panel ,..) can connect to a plc S7-400 cpu417. According Technical Specifications of cpu417-4dp, maximum number of stations that can log on for message functions (e.g. WIN CC or SIMATIC OP) is 16 , communication functions for plc 417-4 Number of connectable OPs are 63 without message processing,16 with message processing.
Can you give me more information about this matter.
What is difference between stations with message processing and stations without message processing?
How many station(wincc,op panel ,..) can connect to a plc 417 and work without problem?

best regard
 
The message processing is for example ALARM-S.
If you do not use ALARM-S, then you can ignore this limitation.
In addition to the max no of connectable OPs, you also have to check the no of connections with a particular protocol.
Apart from that, do you really need that many OPs ?
 
Dear JesperMP
Thank you for reply

I don't get The message processing yet, Is ALARM-S something like alarm logging in wincc or not?Could you give me more examples?
I use Tcp/Ip protocol for connect 11 wincc station (HMI) to a plc s400 cpu 417 ,4 OPs (wincc flaxible) connected using Profibus to that plc also some time one or two persons connect to plc using step7 by Tcp/ip protocol.
Can I Increase wincc station to 13 Safely?

best regards
 
You should consider using server/client setup for the WinCC. In stead of 11 stand alone stations.
1 server, 11 clients, only needs 1 connection.
If you want to increase the amount of clients to 13, it shouldn't matter, because you'll still be just using 1 connection to the PLC.
 

Similar Topics

Hi PLCs.net! I was curious: How many axis can a B&R APC910 control? Is there a hard limit like certain AB controllers? I'm new to B&R, so would...
Replies
0
Views
368
We are in the process of upgrading our PLC5 machines from Devicenet blocks with analog (current) inputs. We are looking at going to IO Link, due...
Replies
9
Views
2,561
I have an existing Compact Gaurdlogix PLC with exising PointIO on it (Some safety and some standard). We will be adding a new panel with more...
Replies
6
Views
3,313
Hello Everyone, What is the maximum number of window creation possible wonderware intouch ?
Replies
0
Views
1,407
Hello, I'm working on a Schneider Electric Modicon M580 system which is on a 7-slot backplane with 3 NOC cards used for it's DIO network. I've...
Replies
2
Views
2,368
Back
Top Bottom