See the really rough sketch of a motor starter with H-O-A switch. Saw the PLC inputs wired this way twice recently. The AC from the starter cubicle, which has its own transformer, is powering the input signals. The reference (com) on the input card (AB 1769-IA16) if from, of course, a different neutral. Of course this works, but isn't that essentially making the bonding system the return path? I prefer to add a separate contact to monitor each switch position, using the input supply power from the PLC panel. I assume when the above method is used, it is the "cheap and dirty" solution? Thoughts, please? I know there are isolated input cards, and relays could also be used, and there are other issues with doing it this way...but I am seeking thoughts on the AC references. Thanks!!

Snag-0191.jpg
 
My thought would be to add contacts to the switch and keep the two circuits seperate. This way you don't subject the PLC inputs to the inductive noise the 120VAC motor is likely to induce. Just my two cents worth.
 
I agree with the separate contacts; the isolation eliminates a bunch of potential power issues. Another thing to mention is that the "hand" input would come on whenever the PLC contact closes in "auto" mode if wired as drawn.
 
I had to deal with a whole MCC full of starters connected this way, but at least they ran a neutral wire down there to keep from bridging input common through ground!

In my case, they also ran a wire from between the starter coil and the OL contact to detect when it tripped. That input was only true long enough for the PLC to detect it and subsequently turn off it's output. They did not understand why sometimes the alarm showed up in the Panelview when a motor starter tripped, but most of the time, nothing appeared. Since the alarm bit was not sealed or latched, it was just a copy of the input that might be on for a scan or two, there was about a 2 percent chance the Panelview would "see" it.

I never did fix all that mess, but I did manage to trap the faults correctly, because an hour on the keyboard was so much easier than pulling fifty new cables through the plant.
 

Similar Topics

Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
243
Good morning guys; Im new at AB plc, and i just need help about a table or a list called something like "exchange data table" in French it is...
Replies
4
Views
778
What he have is a HMI2GO unit ( KTP900F) and we use a safety relay to trigger our e-stops. What the tech wants to do is guard against e-Stop on...
Replies
2
Views
1,860
Most PLCs are 24v for digital logic, will a Digital input card detect a 12v (automotive) signal as a 1 Looking to do some work on a...
Replies
11
Views
4,300
Hello PLCs.net! I have a kinetix 5500 drive connected to a gantry, I was wondering if there is a way to do active homing using a PLC tag? At this...
Replies
6
Views
3,058
Back
Top Bottom