bluenoser337
Member
See the really rough sketch of a motor starter with H-O-A switch. Saw the PLC inputs wired this way twice recently. The AC from the starter cubicle, which has its own transformer, is powering the input signals. The reference (com) on the input card (AB 1769-IA16) if from, of course, a different neutral. Of course this works, but isn't that essentially making the bonding system the return path? I prefer to add a separate contact to monitor each switch position, using the input supply power from the PLC panel. I assume when the above method is used, it is the "cheap and dirty" solution? Thoughts, please? I know there are isolated input cards, and relays could also be used, and there are other issues with doing it this way...but I am seeking thoughts on the AC references. Thanks!!