PV1000 with a small and medium PLC

Martindag

Member
Join Date
Sep 2009
Location
quebec
Posts
227
Hiya,

I was wondering if you could with a panelview 1000 on (Rsview studio) communicate with a micrologix 1400 on Rslogix 500 ( like on page 1 on the HMI) and the page 2 on a other PLC like a contrologix on Rslogix 5000 ?

I know that we can do multiple PLC for 1 or more HMI all together but can you do it with the PLC dont use the same programming software and are different?.

Thanks !
 
GOOOOOOD question, I had to dig a bit and If you can do this, both processors would have to have the same communication protocol (Ethernet, DH+, DF1) Then I set the communications in the Panelview to look at both processors. Care taken to tag the graphics properly and I do believe that would work. I looked it up and there is a stumbling block, you can use a 1761-NET-ENI that connects to the PLC and convert to Ethernet, problem is it is slow and I believe you can have 3 connections max, so PLC 1, PLC 2 & HMI 3. you just nixed your programmability unless you can connect to your 5000 processor and ride that Ethernet connection in or just disconnect it of you need to program the Micro 1400. I found this out a while back so experimenting is the key! Good Luck
 
Right now i have already a PLC contrlogix working for a system with a panelview 1000, what i want is to modify the HMI with more pages that would also control a other system with a micrologix 1400

Everything would be Ethernet for the control.
 
Last edited:
The standard PanelView+, PanelView+6, Panelview+7 Performance can talk to multiple processors. The Panelview+ Compact and new Panelview+ 7 Standard are limited to 1 communcation with 1 processor only.
 
Helliana, thanks for that concise summary of which PanelView Plus terminals have the single-processor limitation.
 

Similar Topics

I have a mer or apa file for Pv1000 (2711p-rdt10c) and i need convert this files for Pv5000 (2715P-T15CD-K). Are exist a conversion tool for this...
Replies
1
Views
860
Hi, im looking to migrate a 2711-K10C10 to a 2711P-T12W21 Panelview Plus 7 Standard. I migrate the PV1000 application .pba file in FactoryTalk...
Replies
13
Views
1,962
Hi there everyone! Long time lurker, first time poster. I am doing an SLC-5/03 to CompactLogix migration and am having an issue with a barcode...
Replies
1
Views
1,049
Hi, I'm investigating the feasibility of communication between a old PV standard display and a logix L5X controller via the controller serial...
Replies
3
Views
1,459
Hi all, Anyone manage to get this smorgasbord of hardware to cooperate with each other? PLC - Micrologix 1500 1764-28BXBAA CH1 config - DF1 Full...
Replies
2
Views
1,490
Back
Top Bottom