jkerekes is right - the full text to that error is "Unable to open display. Display change is currently controlled remotely" i.e., from the PLC. You've presumably found the link to change a screen using a PLC tag, but as long as that tag is still calling a screen, the HMI won't allow any other screen to be selected.
In general, whenever I set up the remote display number, I also set up the replace display number - which is a PLC tag that the HMI writes to each time it changes the screen. So if the PLC calls for Screen 5, I wait for the HMI to write back that it's showing Screen 5, and then set the remote display number back to zero (which means "I'm not controlling it any more, the operator can select whatever screen they want").
The thing that'll trip you up here is that if you're calling a pop-up (i.e. an on-top display), that won't work - the HMI only writes back the current "replace" type display, not on-top displays. So I always also integrate a 3 second timeout, where if my remote display number is non-zero for 3 seconds, I write it back to zero. In conjunction with this, it's good practice to make all of your remote display calls "one-shotted", so that you don't get stuck where the PLC continuously calls for a screen and won't let go.
Hope that helps!