Red Lion FINS to MODBUS

HamiltonWoods

Member
Join Date
May 2014
Location
US
Posts
3
Good morning. I have configured a Red Lion Data Station Plus to translate between FINS for an OMRON CS1G and MODBUS. In Crimson 3.0 I can add a MODBUS block and pick a digital coil address, but I don't see how to map that coil address to a FINS bit. All I see are word data types. I would like to map individual bits of the CIO memory space to MODBUS addresses (000001 to 65535). Is this possible?
 
I think you will want to set up a write block under your Omron PLC as shown below. Select FINS block and # of elements (words). Once there, right click on a word and expand bits. In the picture, i am moving them to modbus coil addresses.

FINS.JPG
 