Hello
I have a question regarding the absolute encoder.
I have to buy a axis system from Bosch and I think with absolute encoder
When this axis is losing the reference (home)?
When someone moves the axis without power?
With power on and encoder cable disconnected?
Should I make a mechanical mark to move the axis at this mark and set again if the reference was lost?
Thank you
 
one of the advantages of the absolute encoders is that the absolute position of the axis is known by the controller all time
also the homing position is known regarding the presence of the power all time
 
Assuming a 360 count resolution, the encoder has moved 150 counts clockwise. An Incremental Encoder would have given 150 pulses to be counted by an external device. If you lose power to the encoder at this point and assuming the encoder moved another 60 degrees before it came to a stop, the external device would not know that the shaft position is now 210 degrees. However, if it was an absolute encoder that read shaft position and provided a unique value for this position, it will read 210 degrees upon restoration of power.
 
Assuming you are looking at the MSK series motor.

With the M2 feedbak code (Optical encoder multiturn absolute EnDat 2.1) you will get 4096 Motor Turns before roll-over of the signal.

Within each revolution, the feedback will have 2048*2^13 resolution or
16,777,216 bits of resolution. The motor project planning manual lists the accuracy at +/- 20 angular seconds.
 

Similar Topics

Hello. An absolute encoder on a rotary axis gives values in range -2147483648 to 2147483648. When value is > 2147483648 , the encoder value is...
Replies
20
Views
2,296
I have 2 Absolute Encoders 8192 steps per Rev. (Model TR Electronic CEV65m-11003) These Encoders communicate to the PLC5-60 via Parallel push/pull...
Replies
3
Views
1,516
Hi guys I am new to Encoders, so I have limited understanding of how to actually configure it, to the situation that I am in. Using this Absolute...
Replies
2
Views
1,577
Hello to you all! I hope there is someone who can clarify some things to me..... Equipment used: TM PosInput1 (6ES7138-6BA00-0BA0) to read the...
Replies
0
Views
1,270
How to connect the absolute encoder(12 bit resolution) to Hsc module of Slc500 Plc and get raw-data to my ladder logic? Please give me example...
Replies
8
Views
2,697
Back
Top Bottom