It's true that I was given no schematic/drawing of how the components are supports to go together, but there's a maintenance on the robots at one point hope to ask if I can have a look inside the robot to maybe have a better idea. I know this is a bit weird, even I didn't expect this, where I just handed some components/devices and said do make a dispensing system. I really appreciate your help for this.
With the analog regulator you have, generally higher output voltage will equal higher pressure.
This means that when I set the min/max pressure on the ITV2030-312BS3, supplying 0VDC will equal min pressure and +10VDC would mean max pressure from the device. Am I right to say this?
Many valves are not suitable for many liquids. Types of seals, etc., would determine this.
Your valve seems more suitable for moving the cylinder around - extend and retract. And since it's a double solenoid valve, no you cannot just ignore the other solenoid. If you energize solenoid A, the valve will shift and you will have to energize solenoid B to shift it to the previous position.
A single solenoid 2-way valve would be a better choice since it offers on/off (flow/no flow) and no exhaust.
But, then, I am unsure if the valve is for dispensing or actuating the cylinder (in which case it is probably the correct choice).
What my boss wants to do is actually do both of them, so dispense and actuating the cylinder, but for starting this off as you say it's more suitable for
actuating the cylinder, so I will pick this option. So what I have done is connected both valves A and B to the two holes at the side of the CDUK16-200. The image is shown below: I'm sure I did this right?
You will likely need to use some kind of controller with I/O to turn the valve on/off AND a 24 VDC power supply to provide power to the outputs.
So I need a I/O controller that is capable of outputting 24DVC, so that I can control the controller to supply that voltage or not to supply that voltage to the SY3220-5L. Is this Correct, could you please confirm this? Also, can I not just use Adam module +10VDC to control this. If not do you have any suggestions of a controller I/O.
Someone in this form mentioned about using +24VDC for red and -24VDC to control the SY3220-5L. What your opinion about this? I not saying he's wrong but he maybe mistakenly wrote -24VDC instead of ground. I spoke about this to my boss and he's not quite sure about me using that? I though black would be linked to ground and red to +24VDC. Also, on the internet it doesn't mention about -24VDC. Could you clarify this for me please
You used the word 'value' several times in your post - is this a typo? did you mean 'valve' in most all cases?
Yes that was my mistake, it was suppose to be valve, thanks for picking that up.
Thank you for the help you have given me, it's starting to make so much sense now.
Also like to thank you in advance for future help