Hello,
what is the difference between Remote I/O ; Distribute I/O ; Local I/O??
can you please define it

Regards.
 
nope its not home work.
actually i google it . but didnt understand it theory.
i want to understand this.

Ect_09
 
To be confusing, Remote IO (or RIO for short) was also used by Rockwell as the name of one of their distributed IO networks. The term "Remote IO" is often used generically to mean any distributed IO, but it could sometimes specifically mean IO on a RIO network, depending on what system you are using.
 
Thanks rdrast for replying
Sir if Remote and distributed I/O are extenal then what is the difference between these two. why they are naming separately???

Thanks
 
I always use distributed I/O to describe I/O attached to the PLC but in a backplane extension system, remote I/O to mean a dumb I/O island, local on the rack with the CPU on it.
 
Back when

I the old days AB remote I/O was a whole rack ( or part of a rack) around 12"x15"x 18-36" located remotly from the PLC. They then came up with Distributed I/O which was a was smaller around 6"x6"x12" I think and worked in the card level of I/O so you could place them all over the machine or system and just wire them up localy and connect with blue hose. Since then as others have said differant names for the same thing.
 
Local IO - IO in the "local" chassis, which hosts the CPU -- or in nearby additional chassis that are connected in parallel to the local chassis IO bus.

Remote IO - IO in chassis that are not connected to the local IO bus. Remote IO status is transferred to and from the local chassis via a serial interface.

Distributed IO - IO in modules that are not part of a chassis, but are modular units that transfer IO status to and from the local chassis via a serial interface.

NOTE: "Serial interface" may include Ethernet.
 

Similar Topics

I am working with a remote rack with a 1771-ASB adapter, and inside Logix 5000 I am trying to find where it displays the status of each of the...
Replies
8
Views
127
Hi all, recently, I deployed Intouch SCADA to the 7 clients PC, but one PC got pending to update the objects and unable to successful. There is...
Replies
0
Views
47
Something I've never thought about before... maybe you folks have some thoughts or experience. I have a customer that uses a Weidmuller, Modbus...
Replies
3
Views
200
Hi, We have been facing a issue with SCADAPack 474. Configuration is like below. RTU 474 + 6103 PS + 5606 IO Mix Module + 5414 DI Module Only...
Replies
0
Views
84
Hello, Can anyone recommend an expandible IO module with OPC UA? I've deployed the Emerson RSTIO-OM module and it works great, but it has a...
Replies
0
Views
67
Back
Top Bottom